  1. #16
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    326

    Default

    Yes, PVC is acceptable. I would use EMT if it were my house. PVC can get droopy when it sits in the sun. Make sure it is supported to code.

  2. #17
    DIY Junior Member aopainter's Avatar
    Join Date
    May 2011
    Location
    Seattle
    Posts
    10

    Default

    it wont be in the sun. It'll be in my attic, and I'm going to get brackets to tie it down

  3. #18
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,642

    Default

    Use the correct Romex™ wire and skip the indoor conduit...Unless required in your town.


    P.S. And aopainter don't forget the cost to operate the unit, for the electric and chemicals to maintain it.
    Last edited by DonL; 06-01-2011 at 12:45 PM. Reason: P.S.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  4. #19
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,642

    Default

    Quote Originally Posted by ActionDave View Post
    SO should never be run in an attic. It is meant to be used where flexibility is needed not durability. It is never a substitute for permanent wiring.
    Thanks for pointing that out ActionDave,

    How flexible do you think a Type SO 6/3 wire would be.

    I guess you have never worked in the industrial plants, They use it for the big machines and run it in cable trays. And it is very durable, when installed and used in the proper environment.

    How many people have a cable tray in their attic ?

    Jim already said it all, Why don't you catch up.


    O , and have a great day.


    DonL


    P.S. Around here a outdoor Spa / Hot tub is not considered as a permanent fixture. That is why there is no requirement for a building permit. That may vary from area to area.
    Last edited by DonL; 06-01-2011 at 12:34 PM. Reason: P.S.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  5. #20
    DIY Junior Member aopainter's Avatar
    Join Date
    May 2011
    Location
    Seattle
    Posts
    10

    Default

    What is the correct Romex™ wire?

    edit: I looked it up, and I still think it's going to be cheaper to get the cables and run them through PVC Conduit. I can get 6AWG red/blk for $63/100ft, and 8AWG wht for something like $40/100ft, and 12AWG grn/yllw for $30/100ft. Add that to the conduit that I should be able to get under $100, and I can probably run it all for under $300. For $100 ft of 6/3 romex, it runs around that same cost, and my electrician still wants THHW for the outside connection from the disconnect box, to run in EMT conduit.
    Last edited by aopainter; 06-01-2011 at 02:06 PM.

  6. #21
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,642

    Default

    It should be on a ground fault interrupt.


    DonL
    Last edited by DonL; 06-01-2011 at 10:29 PM.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  7. #22
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,642

    Default

    Mixing conductor sizes and colors may be a problem, the ground wire can be smaller, but the other current conductors need to be the same size.

    I hope your project works well.

    Be careful playing with electricity...

    DonL
    Last edited by DonL; 06-01-2011 at 10:33 PM.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  8. #23
    Electrical Contractor Jim Port's Avatar
    Join Date
    Aug 2009
    Location
    Maryland
    Posts
    156

    Default

    I would not change to a smaller size neutral. Some tubs also call for a ground the same size as the other conductors.

  9. #24
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    326

    Default

    Quote Originally Posted by aopainter View Post
    What is the correct Romex™ wire?

    edit: I looked it up, and I still think it's going to be cheaper to get the cables and run them through PVC Conduit. I can get 6AWG red/blk for $63/100ft, and 8AWG wht for something like $40/100ft, and 12AWG grn/yllw for $30/100ft. Add that to the conduit that I should be able to get under $100, and I can probably run it all for under $300. For $100 ft of 6/3 romex, it runs around that same cost, and my electrician still wants THHW for the outside connection from the disconnect box, to run in EMT conduit.
    What size breaker are you tying the 6AWG to? I would guess either a fifty or forty amp breaker. That would mean you would need at least a 10AWG green.

    Jim Port correctly states that some manufactures, a lot actually, want a full size neutral and ground. Check your instructions.

  10. #25
    DIY Junior Member aopainter's Avatar
    Join Date
    May 2011
    Location
    Seattle
    Posts
    10

    Default

    It's a 60 amp Disconnect panel

  11. #26
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Don’t make this more than it has to be.

    Install #4 SE-R al. to the disconnect located on the outside wall and then flex and THW cu. conductors to the tub.

  12. #27
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,642

    Default

    I am glad you stopped by JW,

    I don't think that his friend needs to be thrown under the bus, he is trying to help out.

    And aopainter just wants help, not BS.


    Thank You...
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  13. #28
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    326

    Default

    Quote Originally Posted by aopainter View Post
    It's a 60 amp Disconnect panel
    10AWG copper will work for an equipment ground up to sixty amp.
    Quote Originally Posted by jwelectric View Post
    Don’t make this more than it has to be.

    Install #4 SE-R al. to the disconnect located on the outside wall and then flex and THW cu. conductors to the tub.
    This is another way to skin your cat and would most likely be more economical.

  14. #29
    DIY Junior Member aopainter's Avatar
    Join Date
    May 2011
    Location
    Seattle
    Posts
    10

    Default

    I can't find this cable anywhere online to know what it looks like. I'm going down to the electrical wire store today, so I'll ask about that wire. I was able to get about 90ft of PVC conduit for $17, so i'm going to put that in the attic

  15. #30
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,642

    Default

    Save some conduit for exposed wire outside...

    What wire can you not find ?
    Last edited by DonL; 06-03-2011 at 09:12 AM.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

Similar Threads

  1. Spa Wiring
    By EdGear in forum Electrical Forum discussion & Blog
    Replies: 3
    Last Post: 05-19-2009, 11:19 PM
  2. Re wiring to to 12-2 /14-2
    By solutions in forum Electrical Forum discussion & Blog
    Replies: 10
    Last Post: 03-17-2008, 08:36 AM
  3. Wiring 101
    By MLTHAND in forum HVAC Heating & Cooling
    Replies: 1
    Last Post: 11-13-2007, 03:08 PM
  4. Three way wiring
    By Jed54 in forum Electrical Forum discussion & Blog
    Replies: 17
    Last Post: 08-04-2007, 03:01 PM
  5. Re-Wiring
    By laxnfish4 in forum Remodel Forum & Blog
    Replies: 4
    Last Post: 10-27-2006, 02:33 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •