DonL
Jack of all trades Master of one
It should be on a ground fault interrupt.
DonL
DonL
Last edited:
What is the correct Romexâ„¢ wire?
edit: I looked it up, and I still think it's going to be cheaper to get the cables and run them through PVC Conduit. I can get 6AWG red/blk for $63/100ft, and 8AWG wht for something like $40/100ft, and 12AWG grn/yllw for $30/100ft. Add that to the conduit that I should be able to get under $100, and I can probably run it all for under $300. For $100 ft of 6/3 romex, it runs around that same cost, and my electrician still wants THHW for the outside connection from the disconnect box, to run in EMT conduit.
10AWG copper will work for an equipment ground up to sixty amp.It's a 60 amp Disconnect panel
This is another way to skin your cat and would most likely be more economical.Don’t make this more than it has to be.
Install #4 SE-R al. to the disconnect located on the outside wall and then flex and THW cu. conductors to the tub.
I bought 20ft of EMT conduit for the outside. But the wire I cant find online is "#4 SE-R al." And thats 4AWG right? Do I need 4AWG, i thought 6AWG was what I wanted
This is awkward, but...