  1. #31
    DIY Junior Member aopainter's Avatar
    Join Date
    May 2011
    Location
    Seattle
    Posts
    10

    Default

    I bought 20ft of EMT conduit for the outside. But the wire I cant find online is "#4 SE-R al." And thats 4AWG right? Do I need 4AWG, i thought 6AWG was what I wanted

  2. #32
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,642

    Default

    Quote Originally Posted by aopainter View Post
    I bought 20ft of EMT conduit for the outside. But the wire I cant find online is "#4 SE-R al." And thats 4AWG right? Do I need 4AWG, i thought 6AWG was what I wanted
    If you are putting in a 60 amp service, then you may need #4.

    You might want to see what your current requirements are, and that will determine the breaker and wires size.

    The length does play into the equation, But code seems to play different, That depends on local codes.

    Maybe your friend could make sure that you can meet your code. He should know the requirements.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  3. #33
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    #4 American Wire Gauge aluminum Service Entrance four conductor cable is good for 50 amps. It does not need to be installed in a conduit. Lowe’s or Home Depot will cut to length or any electrical supply house.

    Electrical Metallic Tubing is a bad idea to use for the final connection to the hot tub as the chemicals used in the tub will cause it to rust. Non-Metallic Flex is a better idea for the final run of copper THW conductors.

    Take you age and multiply it by 10 and you haven’t come close to the number of these tubs I have installed in my life time so listen to experience.

  4. #34
    Electrical Contractor Jim Port's Avatar
    Join Date
    Aug 2009
    Location
    Maryland
    Posts
    156

    Default

    The SER cannot be used for the exterior portions to feed the hot tub. The grounding conductor needs to be insulated.

    There is a 6' limit on the flex to feed the tub.
    Last edited by jwelectric; 06-03-2011 at 06:26 PM.

  5. #35
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,642

    Default

    JW is correct, old farts know some stuff.....
    Just meet your local code... And get it done...
    Last edited by jwelectric; 06-03-2011 at 06:28 PM.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  6. #36
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    6 feet from the outside of the tub in the 2011 edition

  7. #37
    In the Trades dwindle's Avatar
    Join Date
    Nov 2012
    Location
    North East Pennsylvania
    Posts
    49

    Default

    Is it legal to have a 3 conductor feed going outside?
    I was under the impression all outdoor 220 fixtures were 4 conductor only.

Similar Threads

  1. Spa Wiring
    By EdGear in forum Electrical Forum discussion & Blog
    Replies: 3
    Last Post: 05-19-2009, 11:19 PM
  2. Re wiring to to 12-2 /14-2
    By solutions in forum Electrical Forum discussion & Blog
    Replies: 10
    Last Post: 03-17-2008, 08:36 AM
  3. Wiring 101
    By MLTHAND in forum HVAC Heating & Cooling
    Replies: 1
    Last Post: 11-13-2007, 03:08 PM
  4. Three way wiring
    By Jed54 in forum Electrical Forum discussion & Blog
    Replies: 17
    Last Post: 08-04-2007, 03:01 PM
  5. Re-Wiring
    By laxnfish4 in forum Remodel Forum & Blog
    Replies: 4
    Last Post: 10-27-2006, 02:33 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •