Not without a 15 or 20 amp breaker to protect the outlet. And not if the spa instructions say "dedicated circuit."
It needs to be GFCI protected. If the 60A GFCI feeds a panel. That panel can have a normal breaker that feeds a normal receptacle. But that's a bad design.
It's not necessary if the 60A GFCI was used earlier in the circuit.
A better design is to use a four or more space panel where the disconnect would go. Do a load calculation and feed that panel with the correct wires. Put a normal breaker in the main panel to protect those wires. Then use the 60A GFCI in the subpanel. It's also the disconnect. In the subpanel use a normal breaker to feed a GFCI receptacle.
This way when 120V loads nuisance trip the GFCI there will be less walking and the spa wont shut off.