Freon Filling steps required??

Users who are viewing this thread

Shahnaimath

New Member
Messages
25
Reaction score
0
Points
0
Location
Saudi Arabia
Hi all....

Can anyone here explain me how to fill freon in a AC unit...What are some of the basic steps that are to be noted while filling freon in the AC unit i.e. suction pressure and discharge pressure readings.

Please help I want to learn as this is very important for me...Thanks:cool:
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
That would depend on the type of refrigerant that you are using, and the type of system you are filling.

Also depends if you are adding refrigerant, or opening up a system, And need to recover the refrigerant.

No easy answer to that broad of a question.

Have a Great Day.

DonL
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
It can get messy, and there are some big fines if you don't do it right. People go to school for awhile to learn how to do it right, so trying to learn here on a forum, just isn't really a viable method...there's too much to cover. There are some general prinicples, but the specifics of an individual unit also need to be taken into account.
 

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
Freon is a brand name which is owned by DuPont. It is being phased out in the U.S. due to environmental concerns.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
I think that outlawing Freon R12 originally, was just to make money.

If the new stuff is so safe then why do you have to recover it ?

Just another way to make the consumer pay more, I think.


DonL
 

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
Actually the replacement for R-12 (R-134a) is more environmentally friendly than it's predecessor, but it's still clearly not good for the future of the planet. A replacement for the replacement will be coming out in the not-so-distant future. It's clearly not over yet.
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
First, you need to draw approx. a 250 micron vacuum on the system to remove all air and non-condensibles which may have gotten in. Hold for a while, to make sure it doesn't creep up much, which would indicate a leak. If the system is empty, you have to weigh in approx. the amount of charge stated on the equipment data plate BEFORE starting the compressor.

Once you are ready to run, you hook up your gauges. You don't charge just by observing suction and discharge pressures. Those are not a fixed number, but will vary with ambient and load. You MUST measure suction superheat ( if using an orifice inside) or liquid subcooling if the unit is a heatpump, or otherwise has a TXV on the inside unit. ONLY the superheat or subcool numbers will tell you if the system is operating correctly, or needs to have the charge adjusted.
 

hj

Master Plumber
Messages
33,602
Reaction score
1,041
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
I think the first step would be to get certified for refrigerant gases, since you cannot buy most of them without it. Cerification would cover reclamation, vacuum purging, refilling, superheat, etc.
 

Shahnaimath

New Member
Messages
25
Reaction score
0
Points
0
Location
Saudi Arabia
@Jimbo

Thanks for the tips...We have a pool heater which works on refrigeration cycle. It is totally similar to an AC unit. The standard suction and discharge pressure readings are 65 and 250 for it. I just need some basic steps for filling R22 if the gas level falls below the mentioned range.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
shahnaimath, do you need a Certification in your country to work on refrigeration systems ?

"if the gas level falls below the mentioned range" then that would indicate a leak, and the leak should be found and repaired, before adding more R22.

Have a great day.


DonL
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
I think the first step would be to get certified for refrigerant gases, since you cannot buy most of them without it. Cerification would cover reclamation, vacuum purging, refilling, superheat, etc.

Unfortunately, hj, EPA certification does not cover any aspects of system maintenance or installation. It is strictly limited to the legalities of not allowing gas to escape, how to keep your log books, etc. Other than a contractor's license for the company owner, there is not any legal requirement ( here in CA at least) for licensure or training of HVAC techs. And there are plenty of shade tree operaors out there!
 

Shahnaimath

New Member
Messages
25
Reaction score
0
Points
0
Location
Saudi Arabia
@DonL

We dont really need any kind of certifications here for filling R22...

Also there may be chances of gas evaporating and this should be one of the causes low pressure values..
 
Last edited:

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
@DonL

We dont really need any kind of certifications here for filling R22...

Also there may be chances of gas evaporating and this should be one of the causes low pressure values..

Systems are completely closed, including the hermetic compressor. There is NO evaporation, even in your climate. If the charge is low, it is because there is a leak.
 

Tom Sawyer

In the Trades
Messages
3,625
Reaction score
34
Points
48
Location
Maine
Well all you EPA and code guys..... He's in Saudi Arabia, doubt that they give a flyin F what spilles into the air over there and even here, the EPA only harasses us licensed HVAC technicians. Homeowners can do any damn thing they want.
 