    Default Washer P-Trap conundrum

    I recently had a plumber redo my plumbing for my shower, tub and washer closet which are adjacent to each other. Unfortunately the guy did not put in a p-trap for the washer as required by the California Code and the challenge is now how to fit in a trap given the tight space and other pipes in the area. I have attached a picture with some measures to give you an idea about the current setup and constraints and would appreciate any and all creative suggestions for how to bring this up to CA code.

    Thanks in advance for your help!
    Attached Images Attached Images  

  2. #2
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,221
    Blog Entries
    1

    Default

    Your "plumber" ran the washer into the tub vent, therefore siphoning the tub trap every time the washer drains, and now the tub vent, which combines with the washer drain is open and allows sewer gas out into the home.

    Someone needs to go below the floor, and add a wye and second line up for the washer. The vent for the tub and the vent for the washer (assuming you add a p-trap this time) can reconnect above the washer box.

    It looks nice, but it's completely wrong.
    Last edited by Terry; 05-20-2011 at 09:44 AM.

  3. #3
    In the Trades Gary Swart's Avatar
    Join Date
    Sep 2004
    Location
    Yakima WA
    Posts
    7,246

    Default

    Your "plumber" is not a plumber. At best he is a handyman and not a very good one at that.

  4. #4
    In the Trades SacCity's Avatar
    Join Date
    Mar 2011
    Location
    Sacramento, CA
    Posts
    189

    Default

    Quote Originally Posted by Gary Swart View Post
    Your "plumber" is not a plumber. At best he is a handyman and not a very good one at that.
    Hay he did beautiful work, its all wrong, but it looks good. Again it is wrong and needs to be redressed. Need to have a trap on the laundry line, ect...
    Michael
    Sac City Plumbing
    http://SacCityPlumbing.com

  5. #5
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,687

    Default

    This is a good example of someone who believes that "as long as it works it doesn't make any difference HOW it is installed". Your "plumber", in the words of Benny Hill, is NOT what he is, just what he calls himself. He did it the "easy way", and there is really NO easy way to do it correctly.

Similar Threads

  1. washer p trap problems
    By mema in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 07-28-2010, 01:50 PM
  2. Washer stand pipe, trap, and drain within one stud bay
    By bsperr in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 8
    Last Post: 05-29-2010, 08:01 AM
  3. No Room For P-Trap on Washer Standpipe
    By DigitalJim in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 08-07-2009, 01:12 PM
  4. floor drain and washer sharing trap?
    By steverino in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 17
    Last Post: 04-14-2009, 03:19 PM
  5. Washer Drain Lint Trap Advice NEEDED:
    By Nana Beans in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 0
    Last Post: 02-06-2005, 08:40 AM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •