    I need flat roof advice / options. I’m purchasing this home and there are minor issues with the flat roof. I never wanted a home with a flat roof but in any case…there is living area beneath this roof.
    I don’t want to be the homeowner that has flat roof leaks that either goes unnoticed or that require constant maintenance. I’d love to convert it into a deck – or am I looking for trouble? I don’t know what’s out there that is tried and true, any ideas? Am I better off having it pitched and using regular shingles or just keeping it as is? I believe it is painted on tar substance – it’s not torched.
    The best flat roof protection is probably a continuous membrane. If you decide you want to tile it, there are several methods that also would waterproof it. The roof needs some slope so stuff doesn't pool and if it can't slope to the outside, needs a drain of sufficient size, with the area sloped to the drain (similar to a shower). www.schluter.com makes a system that is designed to tile an outside roof deck, but if you don't want to tile it, and the area is walked on, you need something else. Most membranes are not designed to be walked on, but many can support an applied, floating wear surface on top of it. Flashing is critical on any roof, but even more so on a flat one, along with proper drainage.
    Architect Spaceman Spiff's Avatar
    Salt Lake City, Utah
    I'd go with a continous membrane, adhered to at least 2" of foam insulation. That way if there is a cut in the membrane it still won't leak. Also, there are special pads for flat roofs so you can sit pavers on top of the membrane safely. They will protect the membrane and allow water to flow underneath, and have shims so that the paver surface is flat. I do this in commercial architecture on a regular basis.
    Spaceman Spiff aka Mike
    DoD Army bjferri's Avatar
    Jun 2007
    Maryland
    Can you be more specific about the membrane to use and 2" of foam insulation? Something I can suggest to a flat roof specialist. Thanks.
    Brian
    Sorry, but a flat roof specialist that can't offer these suggestions, is not a real specialist! Flat roofs are more of a commercial thing, and maybe search in that area verses residential purveyors.
    Jan 2009
    Quote Originally Posted by bjferri View Post
    Membrane roofs are exterior vapor barriers, so the foam helps protect the roof deck & rafters from rot by keeping it above the dew point of the inteior space air in winter, avoiding condensation at the roof deck, making it resilient to air leaks from the conditioned space. But the amount of foam required is climate-dependent, as well as the R value of the insulation in the rafter/joist bays.
    The dew point of 70F 35% relative humidity air is about 40F, so if you keep average temp at the structural roof deck in January stays above 40F with a 70F interior it's enough prevent moisture accumulation at the roof deck. In say, Gaithersburg the outdoor mean temp for January is ~30F so if you have R30 batts or cellulose in the rafters/joists (2x10s, nominally), you need at least R10 in foam above the roof deck to prevent condensation. That would take 2.5" of EPS (bead-board), or 2" of XPS (extruded polystyrene), or 1.5" of polyisocyanurate. In Baltimore the mean January temp is ~35F, so with R30 in the rafter bays you'd only need a minimum of ~ R5 above the roof deck, so 1.5" of EPS or 1" of XPS or 1" of iso would be enough, but you'd have more margin with 2".
    If you had R38 in the rafter bays (2x12s), that's about 25% more R, so you have to scale up the foam by ~25% (3" of EPS or 2.5" of XPS/iso for Gaithersburg, or 2" EPS or 1.25" of XPS/iso in Baltimore.)
    If the rafter bays are empty or don't have full depth batts/blown fiber, measure the full cavity depth and multiply by 3.5" to come up with a number to approximate a full fill of cellulose for calculating your foam-R, then retrofit it with cellulose. That way convection loops impede any interior air from finding it's way to the roof deck in the first place, and during the hours where it's colder than 30F outdoors and potentially condensing at the roof deck, any condensation that forms is wicked up & safely redistributed by the cellulose to dry seasonally toward the interior. If you don't want to mess up the interior with blowing holes it can be drilled & filled from above prior to laying down the rigid foam.
    Jun 2007
    Maryland
    Ahhh - commercial is perhaps the way to go. Providing I can find a commercial company that does residential. Thanks for the above technical information.
    Brian
  1. Ponding on new flat roof
    By yds in forum Remodel Forum & Blog
    Last Post: 06-26-2012, 12:56 PM
  2. Replies: 1
    Last Post: 02-23-2011, 02:30 PM
  3. Water test w/ lead roof vent flashing (aka roof jack) causes indoor shower
    By DavidTu in forum Plumbing Forum Discussion & Blog
    Last Post: 01-31-2011, 08:24 AM
  4. Flat Roof Question
    By Verdeboy in forum Remodel Forum & Blog
    Last Post: 08-19-2007, 02:05 PM
  5. Bathroom Exhaust-Roof Venting Options
    By bjferri in forum Plumbing Forum Discussion & Blog
    Last Post: 08-17-2007, 12:34 PM