Ground Rod Placement

Users who are viewing this thread

SETexas

New Member
Messages
12
Reaction score
0
Points
0
Location
Southeast Texas
I was just wondering if I needed another ground rod at my shed because of how far my shed is from the main ground rod at the house. House electricity.jpg
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
Hello SETexas,

Would not hurt for extra lightening protection.

You can never have to many grounds, In Texas. The Deeper the better.

Have a Great Day.

DonL


P.S. Are You asking, about needing to meet electrical code ?
 
Last edited:

Speedy Petey

Licensed Electrical Contractor
Messages
1,108
Reaction score
9
Points
38
Location
NY State, USA
The distance has nothing to do with it.
If the shed has a sub-panel in it then it REQUIRES a grounding electrode. If it is only fed with a circuit then no ground rod is required, or needed IMO.

In typical AC building wiring ground rods serve VERY little purpose.
 

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
Yea, what he said.

You can only have a single circuit in an outbuilding, UNLESS you have a subpanel in the outbuilding, which would then require grounding rods.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
As pointed out rods are required as well as an equipment grounding conductor installed with the feeders.
Isolation of the neutral from the EGC and the grounding electrode conductor and panel enclosure.
 

SETexas

New Member
Messages
12
Reaction score
0
Points
0
Location
Southeast Texas
OK, subpanel you mean a breaker box? Yes I have a breaker box in shed fed from 100amp breaker in house.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Although called a “subpanel” in the trade there is no such item as “subpanel”

To be correct it is a remote distribution panel.

Call it whatever trips your trigger but it will require a grounding electrode system
 

frenchelectrican

Electrician
Messages
46
Reaction score
0
Points
0
Location
NE Wis / Paris France { In France now }
And if your dirt is very dry, you may need two ground rods 10' apart.

Most place will ask for two ground rods unless you get someone with specal tester to verify if the ground is under 25 ohms { that can get very expensive to do that } so it cheaper just get two ground rods and be done with it and keep the rods at least 2 meter apart { 6 feet } or more.

Merci,.
Marc
 