    Default Installing a Kohler Rite-Temp bath & shower valve, K-304

    Installing a Kohler Rite-Temp pressure balance bath & shower valve, K-304
    Rough in instructions from Kohler with some added tips.

    Most plumbers will remove the cartridge, and solder pipe to the valve body first, and then reassemble the valve. The valve comes with the option to thread on a "female adapter", or to insert copper pipe into the brass body of the valve. I prefer to solder copper pipe to the valve.



    two


    two, The pipe to the tub spout needs to be full size. No PEX here. PEX is undersized for a tub spout and will force water up toward the shower head. Either copper or threaded pipe like galvanized or brass. I use either copper or brass. Galvanized will rust and the first time you open the faucet in the morning, you will get some rusty water.



    three, if you have a back to back installation like below, you can reverse the valve without making the pipes cross over.



    four
    Last edited by Terry; 05-02-2011 at 09:20 AM.

  2. #2
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,191
    Blog Entries
    1

    Default



    five



    six



    seven



    eight

  3. #3
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,191
    Blog Entries
    1

    Default



    nine



    ten



    eleven



    twelve

  4. #4
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,191
    Blog Entries
    1

    Default



    thirteen



    fourteen



    fifteen


    sixteen
    Last edited by Terry; 05-01-2011 at 12:47 PM.

  5. #5
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default

    One "minor point". Valves which have the option to solder the tubing directly into the valve, have MALE threads, so you would have to use a "female" adapter, NOT a male one, to connect to the valve. And do you really think plumbers or most handymen/DIYers read the directions?

    I just went back and made that edit. It was Sunday, what can I say?
    Terry
    Last edited by Terry; 05-02-2011 at 09:21 AM.

  6. #6
    DIY Junior Member bananavida's Avatar
    Join Date
    Jun 2011
    Location
    Belize
    Posts
    4

    Default K-304-K-NA installed and no water

    I have loads of water pressure however, after installing the K 304 valve and turning on the water nothing comes out except a couple of drips. It's like the flow is restricted somewhere. I removed the pressure balancing unit and confirmed that yup, loads of water pressure.

    Could my pressure balancing unit faulty right out of the box as it seems to be restricting the water flow to the point of nothing coming out?

    I'm at a loss.

    Any help would be appreciated. THanks

  7. #7
    Consultant cwhyu2's Avatar
    Join Date
    Aug 2007
    Location
    Cincinnati OH
    Posts
    1,330

    Default

    Is it a tub and shower Or shower only? If shower only check restricter in shower head.

Similar Threads

  1. Water supply and pressure with Kohler Rite Temp valve.
    By Designie in forum Shower & bathtub Forum & Blog
    Replies: 6
    Last Post: 10-27-2010, 02:36 PM
  2. Problems with Kohler 304-KS-NA Bath and shower Rite-Temp Valve with stops
    By j_and_c in forum Shower & bathtub Forum & Blog
    Replies: 4
    Last Post: 03-23-2010, 10:02 AM
  3. problems with kohler Rite-Temp shower valve
    By Annec in forum Shower & bathtub Forum & Blog
    Replies: 8
    Last Post: 10-02-2008, 03:57 PM
  4. Kohler Rite-Temp 304 Shower Valve
    By basementshower in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 03-17-2007, 03:59 PM
  5. Kohler Rite-Temp Valve Disassembly
    By ziggy96 in forum Shower & bathtub Forum & Blog
    Replies: 5
    Last Post: 10-05-2005, 10:02 AM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •