GFI tripping

Users who are viewing this thread

ferd

New Member
Messages
15
Reaction score
0
Points
0
Location
Ohio
Installed a gfi duplex in place of standard duplex. Vent fan uses the same feed. gfi trips when you tune the fan off. Wired the fan direct to the feed, not thru the gfi, but gfi still trips. Any suggestions welcome. Thanks
 

ferd

New Member
Messages
15
Reaction score
0
Points
0
Location
Ohio
Already checked. gfi isn't even in the box to touch anything.
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
Look for an issue with your neutrals. If a neutral connection at the load has a path to return thru the GFI, but also another neutral wire connected, then the current can split and the gfi sees a fault. Or if the current from a different load is returned to the gfi neutral...same thing,
 

LLigetfa

DIYer, not in the trades
Messages
7,497
Reaction score
575
Points
113
Location
NW Ontario, Canada
Some of the sparkies on this forum scoff at me when I say that induction loads can induce a voltage when turned off but that is exactly what is happening. The magnetic field in the motor collapses just like an ignition coil does when the points open. Some motors can act as generators as the rotation inertia diminishes when the power is removed. This can trip a GFCI.

The fact that it is tripping a GFCI when the fan is not protected by the GFCI however sounds very suspiciously like a poor neutral bond or a very long run of light gauge wire.

The common cure for motor loads tripping a GFCI is to use a double pole switch designed to switch 240 volt loads.

http://homerepair.about.com/od/electricalrepair/ss/switch_types_3.htm
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Some of the sparkies on this forum scoff at me when I say that induction loads can induce a voltage when turned off but that is exactly what is happening. The magnetic field in the motor collapses just like an ignition coil does when the points open. Some motors can act as generators as the rotation inertia diminishes when the power is removed.
This is very true and I agree with your comments

This can trip a GFCI.
This is very untrue and I completely disagree.
What makes a GFCI open is an imbalance between the hot and neutral and this alone.

The fact that it is tripping a GFCI when the fan is not protected by the GFCI however sounds very suspiciously like a poor neutral bond or a very long run of light gauge wire.
This again would have no effect on a GFCI. A loose neutral would only open the circuit

The common cure for motor loads tripping a GFCI is to use a double pole switch designed to switch 240 volt loads.
a waste of time and money
 

LLigetfa

DIYer, not in the trades
Messages
7,497
Reaction score
575
Points
113
Location
NW Ontario, Canada
This is very true and I agree with your comments
...
This is very untrue and I completely disagree.
What makes a GFCI open is an imbalance between the hot and neutral and this alone.
...
This again would have no effect on a GFCI. A loose neutral would only open the circuit
...
a waste of time and money
This is pretty much the response I was expecting from you.

What makes a GFCI open is a perceived imbalance between the hot and neutral.

In the perfect world, there would be no difference between theory and practice, but some of us can tell the difference.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
This is pretty much the response I was expecting from you.

What makes a GFCI open is a perceived imbalance between the hot and neutral.
Nothing percieved about it. The little current tap in the GFCI device MUST have a difference in current (not voltage) of between 4 to 6 milliamps before it will open, plain and simple.

In the perfect world, there would be no difference between theory and practice, but some of us can tell the difference.
If you think that an induced voltage from a motor somewhere in a system starting or stopping will trip a GFCI receptacle then you ain't one of those who can tell the difference
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
I have seen MANY drinking fountains, freezers, and refrigerators which trip GFCI's.

I have never seen any appliance trip a GFCI device unless there was something wrong with the appliance.

The NEC has mandated that commercial kitchen receptacles have GFCI protection including the ones that supply power to refrigerators and freezers. Drinking fountains are now required to have GFCI protection.

210.8(B) Other Than Dwelling Units. All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in (1) through (5) shall have ground-fault circuit-interrupter protection for personnel:
(1) Bathrooms
(2) Kitchens
(3) Rooftops
(4) Outdoors

422.52 Electric Drinking Fountains. Electric drinking fountains shall be protected with ground-fault circuit interrupter protection.

If the appliance is tripping a GFCI device then it is time to call the repair man.
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
quote; I have never seen any appliance trip a GFCI device unless there was something wrong with the appliance.

You haven't been in the right places then. I had one customer who had a freezer in the garage with an extension cord to it. When I inquired why, since there was an outlet next to it, they said it had "failed" while they were on vacation and ruinded the entire contents. I told her that there was a GFCI somewhere which had tripped. While searching for it, I found it in the bathroom UNDER a bench, and they had not even known it was there. The same thing happened to my daughter and as she said, "cleaning it up was a nasty chore". An elementary school which I was associated with would have to reset GFCIs when the water fountains had warm water. All of these worked properly after resetting the GFCI, so it was not likely to be a "failure" in the appliance.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
What most are calling a failure is really a failure in design. A properly designed unit will not trip a gfci unless it has become defective (and this does not mean it isn't preforming its intended task - it's just no longer totally safe doing it). The newer devices are designed with this in mind...older stuff, you're at risk. If you buy a new product and it trips, get it fixed under warranty, or have it replaced.
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
Many of us have seen the issues hj talks about. I don't think it can usually be attributed to a fault in the appliance.

What I don't know is this.......are GFI receptacles today a little "smarter", so that for example motor load surges or whatever will not cause phantom trips??
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Every year new technology is being brought forth that improves everything including GFCI protection. In the early days of GFIC there were many issues with them including a high amperage trip of 100 milliamps or more.

What causes a GFCI device to open is a difference in current and induced voltage will not and has never caused any GFCI device to open although those who do not understand the integral makeup of the device will tend to blame any and everything they can think of for a reason.

The chip on the inside of a GFCI device will have two little current tap coils that constantly monitor the current in the two conductors. When there is an imbalance of between 4 and 6 milliamps between the two conductors then the device opens.
These current tap coils cannot and do not read the voltages but do read the current or amps flowing in the conductor. If an induced voltage is in one conductor and does not complete the path to the other conductor then no current will flow the device will not open. If an induced voltage is induced in one conductor and there is a complete path then both conductors will carry the same amount of current imposed by this induced voltage and the device will not open.

For the past 10 years or so if an appliance tripped a GFCI device then it was a fault in the appliance that caused an imbalance in current or in other words it was a defective appliance. This is not to say that when this fault occurred it did not clear itself and no longer is faulting and the appliance is working fine now.

When the GFCI device is somewhere upstream of the appliance such as a breaker in the panel or a receptacle up stream it is very possible that the wiring between the device and the appliance being served was where the fault occurred.

It is the job of the GFCI to keep someone from being hurt by electrical current. At around 2.5 milliamps a person can feel the current and it might be uncomfortable. At 25 milliamps a person is at their let-go threshold and in very much pain. The GFCI device is designed to open somewhere in between these two or at 5 milliamps. Notice that in this paragraph I made no mention of voltage but only addressed amperage.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
You certainly do like to spit hairs and hang on the literal word.

Can you have current without voltage?

No but you can have voltage without current. It is not splitting hairs but the facts.
Induced voltage will not trip a GFCI device
Want to trip a GFCI device there has to be a difference in the current. The voltage plays no role what so ever.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
""Theory only works in a vacuum" , there are just to many unknown variables in every day life."

DonL
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Hypothesis
A hypothesis is an educated guess, based on observation. Usually, a hypothesis can be supported or refuted through experimentation or more observation. A hypothesis can be disproven, but not proven to be true.

Theory
A scientific theory summarizes a hypothesis or group of hypotheses that have been supported with repeated testing. A theory is valid as long as there is no evidence to dispute it. Therefore, theories can be disproven.


Law
A law generalizes a body of observations. At the time it is made, no exceptions have been found to a law. Scientific laws explain things, but they do not describe them. One way to tell a law and a theory apart is to ask if the description gives you a means to explain 'why'.

Above are the definitions of Hypothesis, Theory, and Law as it pertains to science.
Math is a law of science.

The laws of current flow (Ohm's Law) state the difference between current and voltage. Only one of these will have any effect on a GFCI device and it is current.

It is not a hypothesis nor is it theory that current is what opens a GFCI device but it is the law of current flow that states that current will open a GFCI device.

It doesn’t matter if you agree or disagree but the law of current flow does not change, it remains the same. What opens a GFCI device is a difference of 4 to 6 milliamps of current between the conductors.
Agree or disagree will not change this fact of law (Ohm's Law).
 

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
The law always applies, but the Chinese-made GFCI fails often out of the box.

You might need to spend more money.
 