    Default Sizing Kitchen Range Breaker Size & Wire Gauge

    Rewiring small cabin and thinking 30 amp and smaller gauge wire is undersize. How do I calculate correct amperage for breaker. Thinking data (wattage) shold be on back of stove. Then what is the calculation, e.g. watts divided by 80% of breaker size?

    Understand that: 50-amp = 6 gauge, 40-amp = 8 gauge, 30-amp = 10 gauge.

    Thanks.

  2. #2
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,522

    Default

    Quote Originally Posted by chuck b View Post
    Rewiring small cabin and thinking 30 amp and smaller gauge wire is undersize. How do I calculate correct amperage for breaker. Thinking data (wattage) shold be on back of stove. Then what is the calculation, e.g. watts divided by 80% of breaker size?

    Understand that: 50-amp = 6 gauge, 40-amp = 8 gauge, 30-amp = 10 gauge.

    Thanks.
    40 amp breaker with 50 amp receptacle is the smallest for a free standing range per 210.19 of the NEC

  3. #3
    DIY Junior Member Benchwrench's Avatar
    Join Date
    Apr 2011
    Location
    Indiana
    Posts
    8

    Default

    40a. breaker w/ #8 Cu. for range or oven.

    Just a note regarding #6 Cu.
    NEC states it's rated at 55a. and allows a 60a. breaker.

  4. #4
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,522

    Default

    But a 50 amp receptacle canít be protected by a 60 overcurrent device therefore the largest overcurrent that can be installed is 50.

    210.21(B) Receptacles.
    (1) Single Receptacle on an Individual Branch Circuit.
    A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit.

    210.3 Rating. Branch circuits recognized by this article shall be rated in accordance with the maximum permitted ampere rating or setting of the overcurrent device. The rating for other than individual branch circuits shall be 15, 20, 30, 40, and 50 amperes. Where conductors of higher ampacity are used for any reason, the ampere rating or setting of the specified overcurrent device shall determine the circuit rating.

    We are told that the receptacle must be as large or larger than the branch circuit and also that the overcurrent device be it breaker or fuse will determine the size of the circuit.

    Ranges come with cords that are either 40 or 50 amps. Using the 40 amp cord and protecting the circuit with a 40 amp overcurrent device is the smallest allowed for any range, see 210.19(A)(3).

Similar Threads

  1. Wire gauge for new double-oven?
    By Artie in forum Electrical Forum discussion & Blog
    Replies: 11
    Last Post: 11-11-2010, 07:51 AM
  2. New range - 3 wire connection
    By Kleggo in forum Electrical Forum discussion & Blog
    Replies: 5
    Last Post: 11-02-2009, 06:18 AM
  3. Installed 240v Dryer, used 10 gauge wire, 20 amp breaker-breakers flicking off
    By 87vertgt in forum Electrical Forum discussion & Blog
    Replies: 12
    Last Post: 10-17-2009, 07:37 AM
  4. wire gauge change mid circuit
    By rockycmt in forum Electrical Forum discussion & Blog
    Replies: 16
    Last Post: 01-09-2009, 11:29 AM
  5. breaker size for 12 gauge wire
    By whoazone in forum Electrical Forum discussion & Blog
    Replies: 9
    Last Post: 10-20-2008, 05:02 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •