You have two different voltages, one 240 volt 30 amp and one 208 volt 30 amp meaning that you will have two cords which is not allowed.
For the branch circuit number 2 aluminum is not large enough unless the calculated load is 90 amps or less.
If using copper then number three would be what is need if the calculated load is more than 85 amps.