    Default Wiring for a 100 Amp Mobile Cart

    Hey All,
    First off, I have no intention of doing a lick of this work myself! I'm just involved with a project and I'm curious about how this is going to get done.
    We're installing a couple pieces of equipment on a mobile cart in a museum. A 220, 30 Amp espresso machine, and a 120/208, 30 Amp Coffee Brewer.

    The cart has a couple other miscellaneous pieces of equipment and they all lead back to a 100 Amp panel in the cart.

    The cart needs to plug into a receptacle in order to receive power...
    I've seen 100 Amp cord caps and receptacles, but I'm curious as to what kind of wiring is going to have to be pulled for the receptacle!? Currently there are two single gang boxes at the location, but they have at the most, 10 gauge solid copper wire in there.
    Is it true that a 100 Amp receptacle will need #2 Wire? Is this going to be a nightmare for the museum to get that size wire pulled through the existing conduit back to the main panel?

    Any discussion would be appreciated. I learn a lot from the back and forth on these forums and appreciate it.

    Thanks,

    Nick

  2. #2
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Welcome to the forum

    You have two different voltages, one 240 volt 30 amp and one 208 volt 30 amp meaning that you will have two cords which is not allowed.

    For the branch circuit number 2 aluminum is not large enough unless the calculated load is 90 amps or less.
    If using copper then number three would be what is need if the calculated load is more than 85 amps.

  3. #3
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    A new 100 amp 240 load is quite an addition....have you checked to see if the panel will support that additional load? And yes, I think # 2 is probably what you need. Our electricians wil give you better info on that soon.

  4. #4
    DIY Junior Member VP Coffee's Avatar
    Join Date
    Apr 2011
    Location
    North Carolina
    Posts
    3

    Default

    Maybe while we're at it, someone can help me properly verbalize the difference between 220, and 120/208
    The 220 is a two hots and a ground appliance, and the 120/208 is two hots, and a ground, and a neutral (L6-30 bs L14-30). Why do I always have a hard time getting electricians to understand what I'm talking about? Is there a different terminology I should use?
    And in regards to the supply, I sure hope they're able to accommodate! This is a new construction and they were informed a long time ago. Problem is, the cart wasn't around and sometimes specs just aren't enough.

  5. #5
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by VP Coffee View Post
    Maybe while we're at it, someone can help me properly verbalize the difference between 220, and 120/208
    220 or 240 will come from a delta transformer and 208 will come from a wye transformer.
    208 will be 120 per leg to neutral and 240 will be 120 to neutral on two legs and 208 on the high leg
    Quote Originally Posted by VP Coffee View Post
    The 220 is a two hots and a ground appliance, and the 120/208 is two hots, and a ground, and a neutral (L6-30 bs L14-30).
    The appliance will mandate if a neutral is needed in either a 240 volt or 208 circuit. You and God only knows what you are talking about with (L6-30 bs L14-30).

    Quote Originally Posted by VP Coffee View Post
    Why do I always have a hard time getting electricians to understand what I'm talking about? Is there a different terminology I should use?
    Maybe so
    Quote Originally Posted by VP Coffee View Post
    And in regards to the supply, I sure hope they're able to accommodate! This is a new construction and they were informed a long time ago. Problem is, the cart wasn't around and sometimes specs just aren't enough.
    You said in your first post that both of these appliances goes to one 100 amp panel. If this is true then either the 240 or the 208 voltage will be used not both.

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default

    Normally a system has either 208 or 240, but not BOTH. In most cases the appliances can run on whichever you have, but the performance may be different depending on the appliance and which power you have. The wire size to the outlet will be determined by the amp load on the panel, and the circuit breaker feeding it, and NOT necessarily the main breaker in on your "cart". Is the coffee brewer 208 OR 120, or does it have a 208 heater and 120 v. control circuit? How many wire connections does it have? Two or three plus the ground?

  7. #7

    Default

    Quote Originally Posted by jwelectric View Post
    You and God only knows what you are talking about with (L6-30 bs L14-30).
    L6-30 = http://www.amazon.com/Powertronics-N.../dp/B004FVR1HA
    L14-30 = http://www.amazon.com/Socket-NEMA-L1.../dp/B001TQAODC

    -God

  8. #8
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    I should have known that but for some reason my mind went to line 6 30 amp and line 14 30 amps.

    Thanks for the heads up

Similar Threads

  1. Are mobile home sinks different?
    By griffy335 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 10-16-2008, 06:41 AM
  2. Moentrol 3330 - pulling cart prior to soldering?!
    By nivlek in forum Shower & bathtub Forum & Blog
    Replies: 14
    Last Post: 02-09-2008, 09:51 AM
  3. mobile home wall removal...
    By goldenroadrunner in forum Remodel Forum & Blog
    Replies: 0
    Last Post: 03-19-2007, 12:05 PM
  4. New shower in Mobile home
    By Pewterpower in forum Shower & bathtub Forum & Blog
    Replies: 3
    Last Post: 09-17-2006, 07:09 PM
  5. Mobile Home Water Supply