Anyone use these Dow insulation boards for interior walls? I'm thinking about using them in my place. 60 year old Pennsylvania house, exterior brick face over blocks. Currently no interior insulation between block wall and drywall, just 3/4" wood strips between drywall and block. I'm thinking about gluing these foam boards between the wood strips then attaching drywall to the strips. Any issues with moisture being trapped causing mold? The rooms are above ground. I've read some forums where people don't like attaching these boards directly to masonry walls, causes mold, but they are usually referring to basement walls. I've contacted DOW but they say it is OK but they recommend air space between the foam board and drywall.
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
You would want a vapor barrier in the wall. The only way to get an air space with 3/4" furring strips would be to use 1/2" panels and they would probably have such a low R value that they would be almost worthless.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
Foil-faced iso like Tuff-R IS a vapor barrier, which can be both good & bad, but in this case maybe good, but it depends. Is there's a cavity/gap between the brick face and the block wall? How are the floor/ceiling joists mounted to the block?

Mold & moisture problems are only created when moisture can get to the wood, but can't leave. Before insulating, air leaks and vapor diffusion through the gypsum on the interior reaches the cold block wall and condenses when the block is below the dew point of the interior air (typically 35-40F, depending on how warm & humid you keep it indoors), but the block can wick it in without damage, and releases it quickly when the block warms up. After insulating between the gypsum & block the block stays colder (much much colder), and as it's humidity rises, puts the furring and joist connections at risk. With a good air seal on the foam the volume of diffusion & air transported moisture is small, and if there's a vented cavity between the block and brick moisture will be released to the outdoors over time, even in winter. With a cavity-wall the overall performance would be enhanced with an interior vapor-barrier (like foil-facers on Tuff-R), but with a solid masonry wall moisture drives from the exterior during the spring/summer/fall could be much worse than the winter drives from the interior through 3/4" of XPS. While XPS allows more moisture into the block via vapor diffusion in winter, it allows several orders of magnitude better drying toward the interior. Since the block is mostly impervious to the wintertime moisture drives (unlike wood-sheathed buildings).

A typical brick-veneer CMU block wall comes in at a whopping ~R2-2.5 if uninsulated, and they leak air. If the block wall is hollow CMU you can typically double that by filling the hollows with a vapor permeable non-expanding injection foam such a Core Fill or Tripolymer. That would be step-1, bringing the wall's R value up to R4-5, which is only about half the R value of a typical 2x4 studwall with R13 batts, but WAY better than R2.

Then...

With a vent cavity between the walls you can safely add 3/4" foil-faced goods between the furring. Without it, use 3/4" XPS (pink or blue board) insulating sheathing, which is semi-permeable to water vapor to allow the block wall to dry toward the interior, lowering the risk to any wood in contact with the block. With either type of foam board you may still have to leave 6" clearances around joist ends to allow sufficient drying depending on how it's attached, but the overall risk is much lower in a cavity-wall than a solid type.

Cut the rigid foam for a loose fit and glue it to the masonry using blobs of foam board construction adhesive, and use 1-part can-foam (Dow Great Stuff, or similar) to seal the edges of the foam-board to the furring. Trim the can-foam flush with the furring with a knife or saw after the foam has cured.

Alternatively you could inject the same vapor-permable non-expanding foam into that mini-cavity as well as to the CMU cores, if the installer thinks they can do it all without stripping the gypsum off the studs. The vapor-diffusion would be about 5-10x as high through the injection foam as through XPS, so this would be best done on cavity-walls only, since cavity walls dry toward the exterior so much better.

With 3/4" of iso (Tuff-R) you'd be adding R4-5 to the center cavity R value, but only ~R3.5 to the whole-wall R value (whole-wall is with the thermal bridging of the furring & framing factored in.) With 3/4" of XPS (typically cheaper), you'd be only adding R3.3-3.8 center cavity, but the it would add ~R3 to the whole-wall R (as would a non-expanding foam injection into that cavity.)

With both a CMU core fill and 3/4" of rigid foam on the interior you'd be bringing the whole-wall R up to something like R8, (nearly that of a batt-filled studwall) but unlike the typical batted studwall it would nearly air-tight, and the conducted heat loss would be 1/4-1/3 of what it is before treatment. It would be enough to FEEL the difference, and would outperform 2x4 studwall built to "typical" standards as opposed to "best practices, air-tight".
 
Last edited:

Jdon88

New Member
Messages
35
Reaction score
1
Points
0
Location
Pottstown PA
Thanks, thats a lot of info to digest, I need to read it a few times. To answer some of your questions:

I don't think there is a gap between the brick and block, I'll see if I can find out for sure. The wall I'm working on right now has the floor and ceiling joists running parallel to the block wall, there is about a 4" gap between the joist and wall. Looking from below, the ends of the floor joists are sitting on top of the basement block wall which is about 4" wider than the 1st floor brick/block combo.

I don't think I'll go with filling the hollow CMUs since I'm not exposing all the walls, just a few rooms one at a time, and it sounds like at lot of effort/expense to do. I may just play it safe and leave out the insulation, I'd rather pay more for heat/cool then risk mold and have to tear it all out again in a few years.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
See if you can't access the wall from the attic to determine whether it's a cavity wall vs. solid. Often the cavity is ventied/open to a vented attic as the means of keeping the wall dry. If the CMU cores can be foamed from the top get quotes. It may be subsidized, and even if not it may be pretty cheap if there's no driling & patching to do.

At the very minimum 3/4" of XPS (extruded polystyrene) between the existing furring is very low risk, and cuts the heat gain/loss by more than half. Better still would be to pull the existing furring and glue up full sheets of 3/4"-2" of XPS (taping the seams with housewrap tape, and foam-sealing the edges), giving up a very few square feet of interior room area. To hang the drywall cut down 3/8" ply or OSB through-screwed to the CMU (horizontally or vertically) for hanging the 1/2" min wallboard. Alternatively use thinner full-sheet OSB and thinner gypsum (1/2" stackup min), which still meet code as an ignition barrier on the foam.

With all of the furring inside the XPS it's at the same temp & humidity as the room, with zero mold risk. Without furring bridging the insulation you get pretty much the full-R, and by using full sheets rather than cut'n'cobble it goes up quicker, uses less foam (less waste), and produces a superior result overall. The full-sheet approach is also lower risk than not insulating, because it puts a vapor retardent insulating layer between the cold masonry and the mold-susceptible wood & paper materials.

Passing up the opportunity to insulate at this time would be crime. It's more than just fuel use- the wall temps will be 5-10F warmer when it's wicked cold out, and it'll be more comfortable even at the same interior air temp. If you don't insulate now you'll be kicking yourself as fuel/utility prices rise, or when you sell the place. This is the cheapest/best time to do it.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
It occurs to me that you may have fairly easy access to the upper floor CMU cores from the basement, which would make a retrofit foam job of the cores pretty easy even if the CMU walls have plates at the top for supporting the rafters. If you google "cmu core insulation foam" you'll find a number of manufacturers and installers.

The mold risk of a CMU core-fill is zero to negative (that is to say, at worst it's zero, but most of the time it lowers the mold risk issues.) Some non-expanding foam manufacturers & installers are pushing the notion that cavity walls can be filled as well, but don't buy into that. Even though it further lowers the risk of mold, it increases the risk of damage to the brick veneer, particularly in cold climates with freeze/thaw cycles, such as PA where spalling of the brick facing and efflorescence/degradation of the mortar would be increased when the bricks can't dry into the cavity.

During a core fill there will be some seepage through gaps/cracks into the cavity, but an accidental full cavity fill is extremely unlikely, but if that happens it's not going to affect the whole wall, and a masonry sealer would mitigate any downside. A once/decade treatment of the exterior with a silane/silex based masonry sealer is a good idea independent of the status of the cavity (or whether it even exists), since that reduces dew & rain wicking of moisture into the brick, while decreasing the exterior drying rate only somewhat. The drier the masonry, the lower the risk to wood in contact with the masonry.
 

Jdon88

New Member
Messages
35
Reaction score
1
Points
0
Location
Pottstown PA
Thanks for the info Dana. I agree that it would be a crime to not insulate at this point but the more I read about this stuff the more worried I got about mold. Another issue I'd like to avoid would limit the total thickness between block wall and drywall to 3/4". If I go beyond that I'll run into issues with the finish trim around the windows not lining up. I looked up XPS boards and local stores only carry 1/2", I guess thats better than nothing.

I googled cmu core insulation, it looks interesting but I wonder how much it would cost. I'm still reading up on that. I don't think there is easy access to the top but maybe from the basement.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
Mold is all about trapping the ing the moisture in susceptible materials, either by keeping them so cold that moisture condenses on them, or limiting the escaper path with vapor barriers. Foil is a vapor barrier, poly is a vapor barrier, XPS is not at the thicknesses we're talking. Only the wood that is in direct contact with the CMU would be cold enough in winter to have an issue, and the drying capacity of 3/4 " XPS is plenty.

The number of condensing hours in January in Pottstown is also quite limited, with mean outdoor temps for the month in the high 20s. The dew point of 68F 30% relative humidity indoor air is 37F- condensation can only occur at the interior side of the CMU when it's at temps below that for significant periods of time. With R2 of masonry on the outside of R4 of XPS, with a mean interior temp of 68F and a mean exterior temp of 28F, the mean temp at the cold edge of the furring is AT LEAST 41F in January and much warmer the rest of the year. (It's actually warmeer than that, because the furring is only about R0.5, not R4.) 3/4" XPS is truly risk free here, even as a cut'n'cobble.

To keep it at 3/4", try this: Strip the existing furring, put up 3/8" fan-fold XPS (sold as siding underlayment), held in place with 3/8" furring made of ripped down ply or OSB through-screwed to the CMU. Then cut & glue more 3/8" XPS between the furrring. That puts R1.9 of thermal & capillary (wicking) break under the furring, R3.8 elsewhere, and is easy to make very air-tight since there are very few seams to seal. Even without the cut'n'cobble layer this may outperform a 1/2" cut'n'cobble between 3/4" furring, due to the extreme thermal bridging of furring in direct contact with the CMU.

Orange box stores carry pink fan-fold 3/8" XPS in most stores.

The installed cost of CMU core foam is less per unit R than XPS in new construction where the installation does not require drilling, and it's all out in the open. It would be slightly more in an attic installation where the cores were readily accessible, more still where there is drilling involved. But get competing quotes/proposals, and check into subsidies- it's not as horrific as you might think (but not cheap, if un-subsidized.)
 
Last edited:

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
Note to Dana, maybe he will want to comment, but I bought some pink fan-fold xps when working in my basement and found that one side of this insulation has a plastic film on it which I suspect would act as a vapor barrier. I chose not to use it below grade for this reason.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
cacher-chick: It's always good to check the permeance -rating of any fan-fold material you put up there. Anything over 0.75 perms would be fine. The spec on the pink stuff says it's over 1 perm, which would be the case for almost any product sold as a siding underlayment. Apparently the protective film facer is also polystyrene, which is orders of magnitude more permeable than polyethylene or foil. This would be fine to use as a a vapor retarder/caplillary break in a below grade application.
 

Jdon88

New Member
Messages
35
Reaction score
1
Points
0
Location
Pottstown PA
You may have already answered my next question. I bought some XPS at Lowe's and noticed a thin clear film on both sides and was wondering if I should remove it. If it is like the pink stuff discussed above I should just leave it on then?
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
You may have already answered my next question. I bought some XPS at Lowe's and noticed a thin clear film on both sides and was wondering if I should remove it. If it is like the pink stuff discussed above I should just leave it on then?

If it's the fan-fold stuff sold as siding underlayment (usually 1/4-3/4" thick), leave it on. If it's white bead-board (EPS) with vinyl or poly facer it's likely to be too vapor-retardent.

SFAIK the only XPS Lowes carries are Dow products, which are blue. (Owens-Corning XPS is pink) They also carry Dow iso, which has an off-white core and foil facers. Foil facers cannot be used. Lowe's also carries Perm-R EPS (bead-board) both with/without foil facers- if it's the clear polyproyplene facer only (no foil), you're looking at 1.2-2.2 perms, which would be fine in one layer, but would push the limits in a double-layering. (The R-value of EPS bead board at would be R1.5 @ 3.8", or R3 @ 0.75".)
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
I'll have to take another look at it, I didn't see Dow on it. It is blue with Lowe's logo, I'm sure someone made it for them. Actually here's a link to it...http://www.lowes.com/pd_304091-210-...s_ord_nbr|0||p_product_quantity_sold|1&page=2

Pactiv is probably the #3 manufacturer of XPS in the US, usually selling it under their "GreenGuard" trade name. I'd assume the blue ship-lap goods they run for Lowes is similar or identical to their SLX product line, which has no specified perm rating that I could find. Their standard insulation board line spec 0.8 perms for all of thier thin goods, independent of thickness. This is probably due to a lower perm facer, since unfaced XPS would be 2+ perms at 1/2". Unfaced 1" XPS is typically ~ 1.1-1.2 perms, half-inch unfaced runs 2.2-2.4 perms, so it's the facer that's adjusting it. (0.7-1 perm is near-ideal value for exterior sheathing between wood siding & OSB or plywood structural sheathing in most US climates, which is probably the most common application.)

At 0.8 perms you're fine, but a double-layer would bring the stackup down to about 0.4 perms, restricting the inward drying capacity of the masonry a bit too much. A continuous R3 would likely cut your heat loss per square foot of wall by half or better though. Tape the seams with housewrap tape, and foam the top & bottom edges for maximum air-tightness.
 

dimmi

New Member
Messages
7
Reaction score
0
Points
0
above grade block insulation

Just finished reading this thread. Great info Dana. I have a couple of questions. I have a cement block wall above grade. This room is pretty cold in the winter. The wall was insulated with 2 inch unfaced fiberglass bat between the 2x2 furring that is nailed into the block, covered with plastic and 5/8" drywall. Ideally I would like to remove the wood strips and cover the wall with 2" xps foam and then studs and then drywall. However, i'm conserned on how to attach the wood to the block thru the foam since I can't see where the screws are going into the block (hollow part or web or mortar joint) and the damage to the block removal will cause. Other option is to leave the 2x2's in place and glue 1.5" xps in between (2x2's are really 1.5") and then drywall.

If the drywall is touching the xps will is absorb the moisture coming thru and get moldy?
Should I use 1" xps leaving 1/2" gap between the xps and drywall?
Any real benefit to doing any of this verses just leaving the 2'" unfaced fiberglass and plastic sheeting?
Any other ideas?

By the way the drywall is down.

Thanks
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
Just finished reading this thread. Great info Dana. I have a couple of questions. I have a cement block wall above grade. This room is pretty cold in the winter. The wall was insulated with 2 inch unfaced fiberglass bat between the 2x2 furring that is nailed into the block, covered with plastic and 5/8" drywall. Ideally I would like to remove the wood strips and cover the wall with 2" xps foam and then studs and then drywall. However, i'm conserned on how to attach the wood to the block thru the foam since I can't see where the screws are going into the block (hollow part or web or mortar joint) and the damage to the block removal will cause. Other option is to leave the 2x2's in place and glue 1.5" xps in between (2x2's are really 1.5") and then drywall.

If the drywall is touching the xps will is absorb the moisture coming thru and get moldy?
Should I use 1" xps leaving 1/2" gap between the xps and drywall?
Any real benefit to doing any of this verses just leaving the 2'" unfaced fiberglass and plastic sheeting?
Any other ideas?

By the way the drywall is down.

Thanks

Strip the existing furring and clean up any high spots in the mortar etc, and GLUE the XPS (use t & g or ship-lap variants, or 2 layers of 1" sheathing with the seams of the layers offset by a foot or so.) Seal the seams of the XPS with housewrap tape or duct mastic for a super-air seal. If you're trying to minimize the loss of room area, use 1x4 or 1x3 furring rather than 2x, and through-screw it to the block wall with 3-3/4 or 4" concrete anchor screws (Tapcon, or similar), 16" on center or so, then mount the drywall to the furring with 1-1/4" screws. Use a masonry-bit and a standard drill motor (not a hammer-drill/roto-hammer) for drilling the CMU. If you use the bit included in the boxes of Tapcons you won't damage the CMU or masonry.

Since it's not bearing a lot of load, the mounting of the furring to the CMU is not critical, but you can't rely on adhesives alone, gluing the drywall to the foam, since the drywall is a code-required ignition barrier for the foam, and must attach to something structural with fasteners. By screwing the furring to the walls, it becomes the code-required mechanical connection to the structural CMU.

Since it's above grade you could also use 2" foil faced polyiso instead of XPS without creating any problems, and get about R13 out of it (vs. R10 with XPS), maybe even a bit more due to the low-E foil facer and the 3/4" air gap of the 1x furring. Seal the seams with 2" aluminum duct tape (aka "FSK tape".) This would perform comparably to a 2x6 studwall 16" o.c. with blown cellulose or R21 batts.

At the moment you have poly vapor barrier with the moisture-susceptible wood furring on the exterior. CMU wicks up rain & dew, then releases it when the sun hits it, causing VERY high moisture levels, even condensation on the poly in summer, and I'd imagine at least some of the old furring shows signs of mold or rot. With XPS or foil faced iso between then CMU and furring there's a vapor retarder between the CMU and wood, and the wood will stay at the temperature & humidity of the interior as long as you don't use any vapor retarders on the interior such as vinyl/foil wallpaper, or heavy oil paints. The 1.5" of compressed batt has an R value of only ~R6 (best case), but with the thermal bridging of the furring and the minimal R value of the CMU itself factored in the whole-wall performance is only about R4.5.

Going from R4.5 to R10 or R13 you BET you'll be able to feel the difference, winter and summer!
 

dimmi

New Member
Messages
7
Reaction score
0
Points
0
Thanks for the quick response. I took your advise and stripped down the existing furring and put up 2 layers of 1" XPS. I used Tyvek tape to seal the seams and Great Stuff foam for the surrounding gaps. The 2 layers worked better than 1. I was able to slip the 1st under the metal electrical conduit and electrical boxes and the 2nd layer was cut around it. Great Stuff filled the cuts around the conduit. I will put 1x3 furring on top of it. The 3/4" gap created between the xps and drywall is just enough space for the conduit.
I am planning on placing the furring 24"OC. ( 4 screws to cmu per 8' strip) Since I am using 5/8" drywall I read that this is no problem. Agree?
Also, 3/16" tapcon or 1/4" tapcon for attaching the furring?
The tapcon instructions/website state that a hammer drill must be used on the cmu in conflict with your recommendation above. I tried a regular drill in the past and it has

By the way. Know an easy way to cut a channel in XPS?
 
Last edited:

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
I guess it depends on how tough your CMU is, but I've drilled hundreds (thousands? maybe not thousands...) of Tapcons into 1950s vintage CMU walls doing EXACTLY this type of retrofit using a low-speed drill motor rather than a hammerdrill. To be sure it would go quicker with a hammerdrill, and the odds of you cracking a CMU block is pretty remote either way.

Since it's not really a structural loading issue, 3/16" Tapcons are fine, as long as they've penetrated the masonry by 3/4" and you have them at least every 16-24". I'm not sure if there's a real fastener spacing spec for it embedded in the code for the ignition barrier aspect, but you do want to keep your walls flat, right? :) A couple of inches of moment-arm isn't going to put a huge stress on the CMU at each fastener with only 5/8" gypsum board.

Setting the furring 24" o.c. with 5/8" wallboard is fine from all points of view (fire-code and wall-flatness).

I've used a table saw to cut dados/channels in XPS before installing it. Not sure how I'd attack it if it were already up.
 
Last edited:

dimmi

New Member
Messages
7
Reaction score
0
Points
0
Thanks again. Appreciate your help. ******* had 100ct boxes of 1/4, 3 3/4" long tapcons fo $14.99! I snapped up the last box.
Last question. The 2" XPS is straight edge. You think it make a big difference verses tonge and groove?
 

Brewcrew10

New Member
Messages
1
Reaction score
0
Points
0
Location
Buffalo, N.Y.
Dana, what would you reccomend for adding insulation to these walls. Previous wall surface was plaster and lath. Walls are approximately 5" thick of solid concrete with diamond mesh sheeting and another 2" of stucco on top of that on the exterior (although we have just furred out and sided the entire outside of the house). Currently the walls are furred out with 3/4" furring strips (which are attached to studs - appears the concrete was poured between the studs some how). After taking down the existing plaster and lath, which was right against the concrete walls, there appears to have never been a problem with moisture. Any help would be greatly appreciated.