I've got a new Zoeller 1/2 HP pump running fine, accompanied by a Watch Dog battery backup, both connected to separate outflow pipe that Y inside the pit, with a check valve about 18 inches about the pit lid. Problem seems to be that this time of year when ground is still saturated from spring thaw and early spring storms team up, the two pumps can't keep up with the inflow. But the problem's compounded by the amount of water that is pumped into the pit out of the air lock relief hole I drilled in the pipe inside the pit, instead of carrying it past the check valve and on out of the house.
Pump must send water straight up about 8 feet, then horizontally (virtually no slope down, but none up either) about 15" before exiting the house.
My relief hole is only 1/8", but again, it seems to be returning a large percentage of what the pump is trying to remove! Meantime, I've put tape and a clamp over the relief hole to give the pump a leg up, while the monsoon outdoors continues.
Ideas of flaws in my setup?
Pump must send water straight up about 8 feet, then horizontally (virtually no slope down, but none up either) about 15" before exiting the house.
My relief hole is only 1/8", but again, it seems to be returning a large percentage of what the pump is trying to remove! Meantime, I've put tape and a clamp over the relief hole to give the pump a leg up, while the monsoon outdoors continues.
Ideas of flaws in my setup?