    Default Boiler pressure

    I have a boiler in my basement. That does the apartment upstairs it goes up the wall to there ceiling. The building is 2 store and the boiler goes up to the apartment. There's a pressure difference is goes to about 30 psi. When running the thermostat at 70 degrees. Is that cause it goes upstair and goes along distance. Will this hurt anything.??

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,405

    Default

    Depending on the boiler, 30# might be normal, but that seems high for just two stories. To keep the pressure semi-constant, the expansion tank needs to be working. This could be an older style air over water tank, or a newer bladder tank. You may need to replace the bladder tank or purge the old tank to get it to regulate properly. Also, if you have an autofill valve, it could be worn out and letting new water into the system. And, if you have a tankless coil, it could have a leak in it, raising the pressure.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,940

    Default

    30 lbs is where the relief valve does it's thing so no, the system pressure should not be any higher than 15 lbs. Drain or replace the expansion tank. If the pressure still climbs test the auto fill or for a leak in the hot water coil if you have one.

  4. #4
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,405

    Default

    Most residential boilers use 30# relief valves, but there could be a higher pressure one there in an unusual circumstance. Normal operating pressure is typically in the 15# range. A failed expansion tank will cause the pressure to rise, often enough to cause the relief valve to open.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

Similar Threads

  1. Boiler operating pressure
    By rockycmt in forum HVAC Heating & Cooling
    Replies: 7
    Last Post: 11-29-2010, 05:52 AM
  2. H/W Boiler High Pressure
    By jasonnewyork in forum HVAC Heating & Cooling
    Replies: 3
    Last Post: 10-21-2010, 02:10 PM
  3. boiler pressure
    By frank in ohio in forum Boiler Forum
    Replies: 5
    Last Post: 11-24-2009, 09:57 PM
  4. Boiler pressure
    By swcooper in forum HVAC Heating & Cooling
    Replies: 6
    Last Post: 03-31-2007, 10:29 AM
  5. Boiler Pressure Problems
    By DeadlyTedly in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 02-12-2005, 11:41 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •