Is it out of the ordinary or not allowed to switch (2 switches, 2 gang box) both the black hot and red hot conductors with 14/3 cable?

I'd like to run power to the 2 gang box from the panel, then run 14/3 from the 2 gang box to the vanity light, and from there 14/2 for the exhaust fan.
 

SacCity

In the Trades
Messages
188
Reaction score
1
Points
0
Location
Sacramento, CA
Website
saccityplumbing.com
Sounds good,
On my work I would generally run 14/2 on the power leg and 14/3 on the switched legs. Gave me the option of switching lights and fans separately, also made it easier to wire up the boxes if I had a 14/2 I knew it was the power into the box, and if I had the 14/3 I knew it was going out of the switch to the fixture.
Michael
 
Last edited by a moderator:

Dlarrivee

New Member
Messages
1,150
Reaction score
0
Points
0
Location
Canada
Sounds good,
On my work I would generally run 14/2 on the power leg and 14/3 on the switched legs. Gave me the option of switching lights and fans separately, also made it easier to wire up the boxes if I had a 14/2 I knew it was the power into the box, and if I had the 14/3 I knew it was going out of the switch to the fixture.
Michael

That is exactly what I'm planning to do, I figure it would be a cleaner installation that way. I only need 2 feet of 14/2 to go from my light box to my fan this way...
 