Thread: Taco 571-2 Wiring

  1. #1

    Default Taco 571-2 Wiring

    I've been working on a large upstairs project for about a year. Yesterday I opened the valves for the hot & cold water to the bathroom - quite a good feeling. All of my plumbing is complete for the hydronic baseboard heating right to the boiler. As soon as I get the flow valve wired I'm ready to throw the final lever.

    My existing setup was 3 Taco 571-2 valves (two for heat zones and one for domestic hot water). I have added a 4th Taco 571-2 flow valve for the upstairs zone. All four valves are next to one another. I am using a Honeywell RTH4300B thermostat for both the heat and a/c in this zone. The a/c is using four of the terminals on the thermostat.

    There are three terminals on the flow valve. From what I can determine from the instructions, terminal 1 and 3 get connected to the thermostat and terminal 2 is connected to the transformer. There appears to be a 4th wire from the transformer that jumps across terminal 3 as well. I assume I can just jump the #2 & #3 terminals from the flow valve next to this new valve.

    So I think the white wire gets connected to the W on the thermostat and runs to terminal #1 on the flow valve and the Red wire gets connected to the R on the thermostat and then goes to terminal 3 on the valve. Do I simply jump terminals 2 & 3 from the neighboring valve?

    I'm sure this is simple...but I just want to get it right.
    Last edited by Gary in NJ; 08-22-2011 at 07:56 AM.

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    23,717

    Default

    Whether it is "simple or not" depends on HOW the rest of the system is wired. The thermostat SHOULD operate the zone valve, which in turn SHOULD turn on the burner and the circulator. BUT, the system could be wired for constant temperature and pump operation with the thermostat just opening and closing the zone valve. OR constant temperature with the thermostat also operating the pump.
    Licensed residential and commercial plumber

  3. #3

    Default

    OK, looks like I need to do a little more homework here. I'll take a look at how the circulator is wired. I have to tell you, whoever wired this existing system left a real mess. The connections at the transformer is a rats nest.

    I'll trace the wires by color and see how this is wired.

  4. #4
    DIY Senior Member Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,216

    Default

    www.taco-hvac.com

    Has the necessary wiring diagrams. It's too involved to explain here.
    You have 4 zone valves so you either need to 24v 40va transformers or one 24v 60va transformer. Using a single 40va will burn the valve heads out. The easiest way to straighten out and simplify your wiring would be to get a Taco SR504 relay/zone valve controller. It's on their site. Using the SR controller solves your wiring and transformer issues.
    No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license!

  5. #5

    Default

    I need a zone controller even though I only have a single circulator pump? Well, I know when to call a professional...now is that time.
    Last edited by Gary in NJ; 08-23-2011 at 06:56 AM.

  6. #6

    Default

    I called TACO and spoke with customer service. The support tech (John) suggested that I could do one of two things:

    1) Add a second transformer (as Tom suggested), or
    2) I use a ZVC404-2.

    Since I really don't like the rats nest of wires that I have right now, I'm going to go with the ZCV404 option.

    Tom, thanks for putting me on the correct path.

  7. #7
    DIY Senior Member Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,216

    Default

    You are going to like it. It greatly simplifies and cleans up the usual rats nest of low voltage wiring. Tekmar and Argo also make similar products. If you talk to John again tell him he owes me one LOL
    No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license!

  8. #8

    Default

    I finally got around to installing the ZVC404. What a straight-forward and easy job. The most difficult part (not that it was) was identifying which wires in the transformer rats nest were Zone 1 (living area) and which were Zone 2 (bedrroms). With that all sorted out (with a multi-meter) I removed all of the existing wires and started from scratch, making sure that everything was properly labeled for future reference. I checked all 3 heating zones and the DHW zone and they all worked. With 4 full baths in the house having the Priority switch for the DHW is a nice feature too.

  9. #9
    DIY Senior Member Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,216

    Default

    Hurray and hazzah
    No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license!

Similar Threads

  1. taco 557 valve
    By pauloden in forum Plumbing Forum Discussion & Blog
    Replies: 0
    Last Post: 03-05-2011, 06:48 AM
  2. Boiler Wiring (Weil CGa, Tekmar 256, Taco SR501, and T-Stat)
    By xjmllc in forum HVAC Heating & Cooling
    Replies: 21
    Last Post: 11-30-2008, 12:45 PM
  3. Wiring a taco zvc404
    By gas696 in forum HVAC Heating & Cooling
    Replies: 1
    Last Post: 11-21-2008, 09:09 AM
  4. taco circulator wiring
    By litemine in forum Plumbing Forum Discussion & Blog
    Replies: 1
    Last Post: 11-25-2007, 03:28 PM
  5. Wiring Taco SR 504 to start two pumps
    By patsfan in forum HVAC Heating & Cooling
    Replies: 0
    Last Post: 11-04-2007, 06:29 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •