Convert Plug-in to Hard-Wire Connection

Users who are viewing this thread

Vistaman

New Member
Messages
35
Reaction score
1
Points
0
My 18 year old 30 gallon electric water heater (240v/3500w) now plugs into a wall receptacle served by a 20a double breaker. The water heater just gave up the ghost and started leaking. The replacement is a similar sized/similar powered unit but code now specifies that the connection should be hard-wired.

Do I just remove the existing plug cover and receptacle, wire nut the new wires into the box, pass them through a metal face plate into bx joined to the face plate, then to the water heater? The service to the water heater is with #12 wire in rigid conduit to a metal box at the wall.

Is that the proper way to convert this setup or is there some other consideration/material to use that make it a proper connection?

Thanks...Stan
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Stan
Two things comes to mind here. First is the new water heater a 3500 watt? If it is a 4500 watt water heater the #12 will be to small. Second, is there a disconnect for the water heater within sight and no more than 50 feet away or a lock out on the breaker? If not replace the receptacle with a no fuse disconnect and proceed
 

Vistaman

New Member
Messages
35
Reaction score
1
Points
0
Thanks for a quick response :)

Yeah, the new unit is 3500 watts. The breaker is only 20a with #12 wire, so that is about the max I can put in. Well maybe a 3800 watt unit would be borderline OK. That means that without upgrading the circuit to #10 and a new breaker, I'm stuck with 3500w. The water heater is in a closet on the patio of our townhouse/villa. It is about 5' away from the main panel which is just inside the front door of the villa. There is /no/ disconnect in the closet. I suppose the "disconnect" on the existing water heater was one of those "pull the plug out" styles of disconnect :) So I guess I will need to use a no fuse disconnect. I'll have to shop for something like that, do you know if it would fit inside the existing box or on top of the existing box?
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
A plaster ring and a 20amp toggle (light switch) will work great. Using an extension ring on the existing box (assuming it is a 4 square) gives access for the cable to the unit to be attached
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
Just make sure the switch is a two-pole version (so it can switch both legs), and rated for the load.
 

Vistaman

New Member
Messages
35
Reaction score
1
Points
0
That's a nice approach. I was thinking I would have to find a large style of non-fusible disconnect metal box like are used for A/C's. And something like this (appropriately rated/two pole <---Thanks Jim!) would be code-approved by the inspector?
 