    Default Faulty breaker?

    Hi,

    I have a main panel (unfortunately without a main breaker) and a sub panel. The sub panel is fed from the main panel via a dual pole breaker. One red and one black connection with some pretty hefty looking wire.

    When I turn off the dual pole breaker (dual switch connected), the black wire to the panel is no longer hot, but the red remains hot. I see no reason why this would or should happen, except that the breaker has failed. Can anyone concur that breakers do fail in this way?

    Thanks in advance.

  2. #2

    Default

    Well, anything is possible, but I've never seen a breaker fail that way (and I've seen more than my share of bad breakers). More likely you are using a cheap DVM to determine if there is voltage present or not. They are notorious for returning bad readings when no voltage is present. You need a 120/240 volt circuit tester such as http://www.drillspot.com/products/73...Voltage_Tester or a analog multimeter if you can find one.

    Also, your main disconnect is probably at your meter.

    -rick
    Last edited by drick; 03-19-2011 at 10:55 PM.

  3. #3
    In the Trades SacCity's Avatar
    Join Date
    Mar 2011
    Location
    Sacramento, CA
    Posts
    189

    Default

    It is possible for the contact to have welded shut, but does not happen frequently, be careful when working on the system.
    Another possibility is a bad neutral on another circuit, which could feed back through that circuit.
    Michael
    Last edited by Terry; 04-06-2011 at 09:27 PM.

  4. #4
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Residential breakers typically have a 10,000 amp interrupt rating. I suspect "welding" of contacts is rare.

    Are you measuring 240 between red and black with it off? How are you measuring the red wire?

    There is probably something else going on. Needs some detective work.

  5. #5
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,678

    Default

    A double pole breaker breaks both legs so you should not be seeing voltage on either side. I have to wonder how you are testing. If using one of those contactless testers, they are notorious for giving false positive results. Athough I've never seen them give a false negative,

    Last line deleted as it is very unsafe
    Mike
    Last edited by jwelectric; 03-20-2011 at 08:49 AM. Reason: safety

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,632

    Default

    IF the breaker was going bad the contact could have overheated, or arced, and welded the switch together. You also have to consider whether there is any chance that you could have a cross connection somewhere that could be "backfeeding" the power into that part of the system.

  7. #7

    Default

    This is a condition normally asociated with FP breakers a replacement breaker is the fix.

  8. #8
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,258

    Default

    I just tested my main 3 phase breaker at the pole and it Doesnt work at all. Will not shut off. Stuff gets old and tired.

Similar Threads

  1. Faulty Faucet?
    By swalsh in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 10-31-2007, 08:35 PM
  2. Faulty Faucet?
    By swalsh in forum Shower & bathtub Forum & Blog
    Replies: 1
    Last Post: 10-31-2007, 01:04 PM
  3. Faulty Faucet
    By AL_2007 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 02-23-2007, 11:31 AM
  4. How to determine which is faulty? CB or Pump?
    By Propwash in forum Pumps and Tanks Well Forum & Blog
    Replies: 3
    Last Post: 11-30-2005, 04:25 AM
  5. Faulty or Frozen Sillcock
    By gumly in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 06-16-2005, 01:39 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •