    Default Why does the vent have to be above the flood level rim?

    I understand that vents are needed to prevent vacuums from forming because of negative air pressure and thus prevent the traps from draining. I don't understand why the vent needs to be six inches above the flood level rim. It seems like allowing air in, at any height, as long as it is downstream from the trap, would relieve/prevent the vacuum. Can someone explain this to me in dummy terms?

  2. #2
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,192
    Blog Entries
    1

    Default

    If the sink backs up, then the vent fills with water and is no longer a vent.
    The vertical sections drain away the solids well, but the horizontal sections don't. Therefore, code wants the horizontal unwashed sections to be above the flood plain. It's the long term solutions to keeping the system up and running no matter what.

    Imagine if Japan had placed their infrastructure above the flood plain. It just makes sense to prevent water problems in the future. If those sections of pipe are where the sludge and water can't collect, then they will last as long as the home.

    There are some cases where inspectors will allow piping with waste fittings below the flood level.

    Here is a nice link to Bert Polk's plumbing tips
    Last edited by Terry; 03-18-2011 at 01:20 PM.

  3. #3
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,937

    Default

    I was just gonna go with because we say so.

  4. #4
    DIY Senior Member dlarrivee's Avatar
    Join Date
    Jun 2009
    Location
    Canada
    Posts
    1,172

    Default

    If you have to ask, then you probably shouldn't be doing your own plumbing...

  5. #5
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,676

    Default

    Quote Originally Posted by Terry View Post
    There are some cases where inspectors will allow piping with waste fittings below the flood level.
    My kitchen sink is in front of a window and the sill is too low to allow the vent to be the required distance above the rim. The inspector made an exception.

    Free standing tubs are another case.

    Last edited by Reader Review; 03-18-2011 at 05:32 PM.

  6. #6
    In the Trades SacCity's Avatar
    Join Date
    Mar 2011
    Location
    Sacramento, CA
    Posts
    189

    Default

    The other option would have been to use a longer trap arm, with the drain running off the side of the window and run the trap arm to under the kitchen sink. I've even seen in some houses where they just run this drain flush along the studs and notch th cabinets around the pipe.....
    Michael

  7. #7
    DIY Senior Member dlarrivee's Avatar
    Join Date
    Jun 2009
    Location
    Canada
    Posts
    1,172

    Default

    Quote Originally Posted by LLigetfa View Post
    My kitchen sink is in front of a window and the sill is too low to allow the vent to be the required distance above the rim. The inspector made an exception.
    Usually there's just a longer trap arm and a typical vent/drain beside the window actually...

  8. #8
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,676

    Default

    The vent went vertical up to the window sill and turned sideways to go around the window where it went vertical again. The horizontal section was above the rim of the sink but the inspector noted that it was not 6" above as required by code.

    {edit}It was a wide mulled pair of windows, much wider than the sink base cabinet so the trap arm would have had to be much longer and be routed through an adjacent base cabinet. Around here they don't let us do side turns on the same plane so I could not jog the trap arm unless I rolled a pair of elbows.
    Last edited by LLigetfa; 03-19-2011 at 06:10 AM.

  9. #9
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Quote Originally Posted by tmpusr889 View Post
    ............... why the vent needs to be six inches above the flood level rim.?
    The take off for the vent isn't the issue. It is that a vent pipe can not be HORIZONTAL below that 6" number, for the reasons explained by others. The vent has to take off, and rise on at least a 45 angle.

  10. #10
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,615

    Default

    You only quoted HALF of the requirement. The other part is 'or 42" above the floor whichever is HIGHER'. That requirement is so you cannot put it a 21" for a toilet and then later install a 36" high sink on that line and expect it to be legal.

  11. #11
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,937

    Default

    Massachusetts still allows flat venting IIRC

  12. #12
    Lost in Never Never Land tmpusr889's Avatar
    Join Date
    Mar 2011
    Location
    Rhode Island
    Posts
    6

    Default

    Thanks, Terry. The link was helpful and I forgot about backup issues.

    I still have a question though. If the vent branches are at 45 degrees and are allowed to drain and the main vent is above the flood plain, shouldn't that be enough? Why does the initial rise have to continue until it's above the flood plain? What is wrong with this:



    ?

Similar Threads

  1. Toilet Bowl Water Level Alternates Level and Flush
    By leichte in forum Toilet Forum discussions
    Replies: 3
    Last Post: 09-06-2010, 10:21 AM
  2. Venting below flood level
    By pbr3232 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 03-16-2009, 04:02 PM
  3. Air admittance valve - "above the flood level rim"?
    By schmeel in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 07-26-2007, 07:52 PM
  4. connecting rough-in 3rd level shower, sink and toilet vent stack
    By ajerome44 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 07-01-2007, 10:40 PM
  5. Water level in toilet bowl mystery--vent problem?
    By Buzzbee in forum Toilet Forum discussions
    Replies: 5
    Last Post: 11-20-2005, 09:13 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •