    Question Dryer feed, how far is too far?

    Hello,

    I am considering moving my laundry from the basement to the living level. (Gotta keep the wife happy).

    I have two questions

    1) How far is too far to run 10/3 cable? It looks like I will need about 70' to get from the box to the new dryer point.

    2) If the distance is not too far, do I have to drill every floor joist or can I nail up so 1x4 and surface mount the cable?

    Thank you,
    Fred

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,412

    Default

    First, what size circuit breaker does the dryer require? That, along with the length, will determine what size wire gauge is required. 10g may be too small.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    DIY Junior Member acrscout's Avatar
    Join Date
    Mar 2011
    Location
    Northern Virginia
    Posts
    3

    Default

    Quote Originally Posted by jadnashua View Post
    First, what size circuit breaker does the dryer require? That, along with the length, will determine what size wire gauge is required. 10g may be too small.
    30 Amps 220 v

  4. #4
    DIY Junior Member acrscout's Avatar
    Join Date
    Mar 2011
    Location
    Northern Virginia
    Posts
    3

    Default

    Quote Originally Posted by jadnashua View Post
    First, what size circuit breaker does the dryer require? That, along with the length, will determine what size wire gauge is required. 10g may be too small.
    30 Amps 220 v

  5. #5
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    nail the 1 by then install the 10/3 on top (or bottom depneding on you outlook)

  6. #6
    Electrical Contractor Bobelectric's Avatar
    Join Date
    Feb 2009
    Location
    Eighty Four,Pa. 15330
    Posts
    37

    Default

    Drill It!.......

  7. #7
    DIY Member teamo's Avatar
    Join Date
    Jun 2005
    Location
    Massachusetts
    Posts
    95

    Default

    Use the #10 copper and a 30 amp breaker and you should be fine.

Similar Threads

  1. gravity feed spring
    By Ridgeview Farm in forum Solar and Geothermal Water Heating Forum
    Replies: 2
    Last Post: 10-03-2011, 02:58 PM
  2. gravity feed calculation help !!!
    By YourFinancialPlanner in forum Irrigation / Sprinkler Forum
    Replies: 6
    Last Post: 08-15-2010, 11:58 AM
  3. Stove Hood feed....
    By Rich B in forum Electrical Forum discussion & Blog
    Replies: 4
    Last Post: 04-21-2010, 01:55 PM
  4. Which line to use for water feed?
    By DIYourselfer in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 01-27-2010, 06:57 AM
  5. Want to run new feed to garage
    By arfeller in forum Electrical Forum discussion & Blog
    Replies: 8
    Last Post: 11-26-2009, 09:44 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •