Thread: Is my bathroom vent designed properly??

  1. #1
    DIY Member Gnfanatic's Avatar
    Join Date
    Aug 2008
    Location
    New Jersey
    Posts
    43

    Default Is my bathroom vent designed properly??

    Hey guys, now that my heating system is done I am working on my gutted bathroom. I will be filing for a permit this week and be doing the work myself. I never plumbed a bathroom from scratch before so I am working at one step at a time. The sink, toilet and tub are against the exterior wall. Instead of touching the insulation and drilling holes I am building a another 2x4 wall in front of it for plumbing purpuse's. All vent piping will be 2inch's and it will be 3 inchs in the attic coming out of the roof (6 inchs of roof line). The horizontal pvc is above the sink by 8 inchs. Does this design look right? I know it is very vague, just looking at the basics right now.

    thanks!!!!
    Attached Images Attached Images  
    Ralph

  2. #2
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,201
    Blog Entries
    1

    Default

    The sink can use a 1.5" vent
    The tub/shower can use a 1.5" vent
    The toilet uses a 2" vent

    Revent at least 6" above flood level of highest fixture. That would be the lav.

  3. #3
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,940

    Default

    If he's IPC the entire group can be vent 11/2" for that matter two bath groups can be vented with one 1 1/2

  4. #4
    DIY Member Gnfanatic's Avatar
    Join Date
    Aug 2008
    Location
    New Jersey
    Posts
    43

    Default

    Hey guys, thanks for the reply I truly appreciate it. I am going to call the town today and ask if i can vent everything 2 inchs to make life easier for me. I understand about the horizontal tubing being above the highest flood point at least 6 inchs. The tricky part is the 4 inch drain I need to build runs directly at the bottom of this wall and floor joists horizontally. I will take some pics and hopefully you guys can give me ideas.

    thanks again and have a great day!
    Ralph

  5. #5
    DIY Junior Member Bob Lewis's Avatar
    Join Date
    Feb 2011
    Location
    WA
    Posts
    26

    Default

    While I have gotten good advice from the board I have found the best advice I have gotten is from the person who will be doing the inspection. If you are getting it inspected get a detailed enough drawing of exactly what you plan to do and contact the inspector. In my case the guy was very clear about what he wanted to see and how it would be tested so it took any and all guess work out of the equation.

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default

    In most cases, he will NOT get a permit until he submits a "detailed drawing" of how he intends to install the drains and vents. Vents are easy, ONCE you have the drains installed properly. Our inspectors are NOT in the business of designing plumbing, or any other, systems. They will "reject" incorrect drawings and expect YOU to make any corrections before resubmitting them.

  7. #7
    DIY Junior Member Bob Lewis's Avatar
    Join Date
    Feb 2011
    Location
    WA
    Posts
    26

    Default

    Let me rephrase that then. If you can get a permit without a detailed drawing get the permit and make a detailed drawing and submit it to the inspector. If you can't get the permit first make the detailed drawing and submit it. If it is rejected they will need to tell you why. Fix what they have rejected, resubmit, get it approved, then move on with the plan. Talking with the inspector will also be helpful in that you will know how they plan to test the system. The inspector I have dealt with would much rather have it done right rather than coming to inspect it and have you rip it all out because its not.

Similar Threads

  1. 3 Liter or .8 gallon toilet Canadian designed Proficiency toilet
    By morehp in forum Toilet Forum discussions
    Replies: 14
    Last Post: 07-08-2012, 07:51 PM
  2. Instralled a new g-disposal and re-designed the drain...
    By pmaru77 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 04-23-2009, 05:06 PM
  3. Bathroom Vent - What is best?
    By M Clark in forum HVAC Heating & Cooling
    Replies: 0
    Last Post: 11-17-2007, 10:46 AM
  4. Island style vent for bathroom sink vent?
    By rvportland in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 10
    Last Post: 11-16-2006, 08:34 PM
  5. Can I vent New bathroom vent into dryer vent line?
    By cwolters in forum Shower & bathtub Forum & Blog
    Replies: 3
    Last Post: 04-25-2005, 04:03 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •