Thread: Rinnai 556FA wall furnace failure/error

  1. #1

    Default Rinnai 556FA wall furnace failure/error

    Have a 5+ year old Rinnai 556FAIII Rinnai Gas Direct Vent Wall Furnace. Recently having problems with an error/shut down of unit. About a month ago, the unit went into error mode. I fixed it by pulling the cord and restarting. Now, the unit goes into complete error and restarting will not fix the problem. The unit reads flame failure. Every time a call for heat initiates, the heater will go through its normal startup procedure. I can hear the sparker, see the flame ignite and the blower activate. After about 3 seconds, the flame cuts out and the blower continues runnning putting out cold air. Tried searching the boards with no luck. A service call in my neck of the woods runs $250.00 +. Any help greatly appreciated.....

    Thanks

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,381

    Default

    It is not confirming that the burner ignited, so it is shutting itself off and running a purge cycle. It might repleat that a few times before it shuts down with an error message. The flame sensor itself might be dirty - cleaning it might help. It could be out of position (unlikely unless you'd been in there cleaning things), the flame could be messed up so it is not actually hitting the sensor, the sensor could be bad and needs to be replaced, or the circuit that 'reads' the flame sensor is either bad, or there's a loose connection getting it there.

    Depending on the type of sensor, you may be able to easily test it - it would be described in the maintenance manual. I'd look at it, clean it if it's dirty (maybe some steel wool - depends on the type), and make sure that where it is, the flame actually hits it.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

Similar Threads

  1. Wall Furnace: Pilot does not stay lit
    By ThomasE in forum HVAC Heating & Cooling
    Replies: 1
    Last Post: 03-03-2010, 05:38 PM
  2. Wall Furnace Mystery
    By Mike Armstrong in forum HVAC Heating & Cooling
    Replies: 3
    Last Post: 11-05-2009, 02:40 PM
  3. Type B Vent Cap Height For Wall Furnace
    By turkeyvulture in forum HVAC Heating & Cooling
    Replies: 2
    Last Post: 07-31-2009, 08:38 PM
  4. Rinnai tuning
    By BimmerRacer in forum Tankless Water Heater Forum
    Replies: 1
    Last Post: 07-06-2009, 05:47 AM
  5. Furnace venting inside a wall
    By sctclimbs in forum HVAC Heating & Cooling
    Replies: 3
    Last Post: 10-18-2007, 02:55 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •