Double Vanity Vent

Users who are viewing this thread

handyman923

Member
Messages
36
Reaction score
0
Points
6
Location
Portland, OR
I am remodeling our bathroom and am working on the DWV for the double vanity. I want to recess a cabinet into the wall right where the existing vent goes up. See attached diagram. I would like to cap off this vent and then run a separate vent from each lav up into the attic, and tie them together in the attic. Does everything in my sketch look legal?

I am in Oregon and we use the UPC.

Thanks for any advice!
 

Attachments

  • Double Lav.pdf
    17.3 KB · Views: 273

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
You should not use a sanitary tee on it's back as a drainage fitting.
Instead of a double sanitary tee in the middle, you need a double fixture fitting.
Below the double sanitary tee should be a cleanout tee.
 

handyman923

Member
Messages
36
Reaction score
0
Points
6
Location
Portland, OR
Thanks for the reply!

Instead of the sanitary tee on its back, is it okay to use a combo wye?

Also, is it okay to put a cap on top of the double fixture fitting?
 

Dlarrivee

New Member
Messages
1,150
Reaction score
0
Points
0
Location
Canada
Seems like an awfully convoluted way of going about this...

If you insist on using the double san-tee instead of a double fixture fitting, please for the sake of the drain cleaner install a proper clean out below it.
 

Tom Sawyer

In the Trades
Messages
3,625
Reaction score
34
Points
48
Location
Maine
In that position and because there is an elbow off the tee for the drain itself a san-tee is fine because it is technically being used as a vent fitting. I/E the branch of the tee is dry and does not recieve waste. I would pipe it that way. Depending on trap arm sistances you may not need to run two vents.
 

hj

Master Plumber
Messages
33,608
Reaction score
1,047
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
IF you use the proper fitting, and the two arms are within the maximum permitted, you can use the single center vent and just offset it around the cabinet. Regardless of how you do it, you still need the proper fitting in the center, except using two vents you CAN use a double combo, otherwise you need a "back to back fixture fitting". Either on SHOULD have a cleanout below it.
 