What it sounds like to me is you have what we call a "closed" system and your Temperature/Pressure valve on the water heater is tripping due to water expansion created when the water heat is activated. A closed system is created when there is a check valve in the water supply line that prevents the expanded water from being absorbed by the water main. The check frequently is a Pressure Regulator Valve, but can be in the water meter itself. When water heats, it expands and if this expansion is not dealt with, the pressure in the water heat will rise rapidly and trip the T/P valve which is a safety device to prevent the heater from exploding. When the heating stops, the pressure returns to normal and the T/P closes. The cure for the problem is to install a thermal expansion tank in the cold water supply line between the PRV and water heater. This is an air-charged tank usually about 2 gallon size and this provides a place for the expanded water to reside until the pressure lowers. I think what you refer to a "the little copper line" is the pipe from the T/P valve. It does not, or at least is absolutely should not, connect solidly to the drain, so it does not pressurize the drain, and it should it never drip a water. By the way you describe your problem, it appears you are unfamiliar with plumbing basics, so I would urge you to hire a professional plumber to deal with this problem. It should not require opening walls, and if my diagnosis is correct, installing an expansion tank is quite simple. (It does have to be done correctly however)