    Default Emergency Generator Test with questionable results

    When I remodeled my house about 3 years ago, an electrical upgrade was done that included replacing all non-temperature rated wiring (cloth wrapped, without ground wires) and adding a pre-wired automatic transfer switch with service connection located on the side of the house. The ATS panel is rated 240v/50A and is connected to the main breaker panel via a double pole 50 amp breaker. It has several important circuits on it, including sump pump, refrigerator, freezer, gas burner equipped heat pump, boiler, strategic general lighting circuits, and alarm system. I have not gotten to the point to put in a permanently installed generator, but I do have a portable generator rated 7000 watts with L14-30 connector that matches the service connection to my house for the emergency generator, also a L14-30 connector.

    I recently decided to test this setup and see how it works, so I could see if I am ready for an outage. So, I set the thermostats down on my heating systems and switched my heat pump to emergency heat so it would only run gas heat. Then, I connected up my generator to the house and started it up and let it run for a few minutes to warm up. Next, I threw the 50 amp double pole breaker in my main panel to kill utility power to the ATS. After the 20 second timeout, I heard the ATS pick up on generator power and the emergency circuits came back on. All seems as it should, so I moved on to the next test - filling up the sump pump crock to get the sump pump to kick in and empty out the crock. Before I get the sump crock filled with water, I heard the generator governor kick in and then smelled electrical burning, so I canceled the test and went back and restored utility power to the ATS by resetting the 50 amp breaker in the main panel and letting the generator run unloaded and disconnected to cool down. Found out that the transformers (120v-24v) in both the heat pump and the boiler had burned up and had to replace them. Never even got to do the sump pump test on the generator, but did complete it on utility power, just to make sure the sump pump still works. No other equipment has been identified as damaged in this test.

    So, any thoughts to share on what might have happened that would have burned up those transformers? If there was a surge, wouldn't a circuit breaker on the generator or ATS trip? Would a brown out burn up a transformer? Is it likely that the generator can surge to that level of damage? Granted, the transformers are probably the most sensitive devices in this scenario.

    How should I test this out, without destroying any more expensive parts or equipment?

    Everything is fine now that I am back on normal power and after replacing the burned transformers.

    Any thoughts would be appreciated, and having the system tested by a licensed electrician is also a fair recommendation, but I just want to make sure I have checked all the easy suspects.

  2. #2
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,226

    Default

    These small generators do not have a voltage regulator on them so when the generator goes into a load the voltage varies and a coil does not like this therefore it lets go of its smoke and quits.

    I don’t know how many times I have said that a generator than has receptacles on their frame is not designed for what you are proposing to do. You are looking for trouble each and every time you try to use something designed for a thirty amp load max and putting large surges of starting motors on them.

  3. #3
    DIY Junior Member Igor's Avatar
    Join Date
    Dec 2007
    Location
    Oregon
    Posts
    19

    Default

    My guess is that the neutral and one of the hots were swapped somewhere, so those 120V transformers were getting 240V.

  4. #4
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,226

    Default

    Quote Originally Posted by Igor View Post
    My guess is that the neutral and one of the hots were swapped somewhere, so those 120V transformers were getting 240V.
    Should this have been a neutral problem it would have shown up long before the pump test.

    It was without a doubt the inrush of current due to the starting of the motor. To start a 1/2 horse power 120 volt motor the motor will have an inrush of about 58 amps which is far more than the small generator will deliver.
    When the motor started the load on the generator caused the gasoline motor to load and speed up which in turn caused a voltage drop followed by a surge in voltage that the transformer could not handle.

    Once again, these small generators were not designed to be connected to a house load. The proper way to use one is with the use of cords plugged directly into the devices (receptacles) on the generator.

    On a side note, I have two small generators. I have horses that need water during an extended power outage (24 hours or more). I use the 7500 watt generator to power the well pump for water at the barn. The other generator is used for emergency lighting at the house. This lighting is a table lamp plugged into a drop cord ran to the generator outside. I have no transfer switches connected to my house at all.

    A power outage is a very rare event and one in which my everyday way of living is interrupted and one which I live on a limited amount of electrical use. I do not try to watch TV or surf the internet during these times.

    Should I for some reason or another need more than a cord during a power outage I will purchase a generator big enough to handle the load. What I wouldn’t do is try to haul 17 ton of rocks on a half ton pickup truck or use a portable generator to power my house. Think of it this way and see if it doesn’t make a little more sense than just saying I have a generator and I want to power up this and that during a power outage.

  5. #5

    Default

    I can start my 3/4 HP deep well pump using my 6500W portable generator with my air handler and all general lighting circuits already on. I'll admit it is a close call though, but during an outage the generator can handle this condition 20 times a day.

    I doubt this is an overload problem. It sounds more like someone screwed up. I'd say you have a wiring problem between the generator and your service panel. And I agree with Igor, it is most likely a hot/neutral swap. Do not try the generator connection again until you have it fixed. Consider yourself lucky if this is the problem and all that happened was 2 transformers were cooked.

    -rick

  6. #6
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,238

    Default

    Submersible franklin pump motors have huge service factors, 1.5 -1.8 in some cases, and they are designed to start on LOW voltage.

    Take a look at Franklins AIM manual, they give extreme lengths of wire runs that a normal electrician would laugh at for such small size. I have had to fight with electricians to use the Franklin designed wire runs because they give great cost savings, and provide a soft start, which greatly reduces starting torque, and the associated lifespan reductions with that in a pump.

    Which all means that portable generators are more than adequate to run submersible motors. I ran a 1 HP pump for 3 days non-stop on a 13HP Briggs genset, along with 2 freezers, a fridge and some lights. Although I wired it into the panel in an "emergency" mode. AND adjusted the motor speed-governor under the full load to 240volts, something few ever bother to check.

    It was without a doubt the inrush of current due to the starting of the motor. To start a 1/2 horse power 120 volt motor the motor will have an inrush of about 58 amps which is far more than the small generator will deliver.
    When the motor started the load on the generator caused the gasoline motor to load and speed up which in turn caused a voltage drop followed by a surge in voltage that the transformer could not handle.


    Seems if that were so, 58 amps [?] would have just killed the genset motor. And If it was a cap start blower motor, that load would have been simple for the generator. And I never could get any surge out of any of the gensets that I have used, and its many. The gen set motor slows down and regains speed as the motor begins its turning.

    The OP needs to tell us if his gas heater and boiler were even engaged. He said he turned the thermostats way down, so perhaps there was no motor turning at all.

    Then one must assume that the 120v transformers got a LONG dose of 240volts. Small transformers do not burn up on low voltages induced by a motor starting.

    I am guessing that the OP heard the governor speed UP [reduced amp draw] when the load on the transformers ceased by melting.
    Last edited by ballvalve; 03-02-2011 at 02:35 PM.

  7. #7
    DIY Senior Member Rich B's Avatar
    Join Date
    Sep 2008
    Location
    New Jersey
    Posts
    259

    Default

    The first thing that needed to be checked before the test was the voltage and frequency of the generators output. How many KW is it ? What brand is it? Many decent sized portables DO have voltage regulators. Any quality built unit of about 4-5kw or higher will have a voltage regulator. These regulators are small and can only keep the voltage in the proper range if engine speed is close to correct. 3600 rpm is the usual rpm for a small unit and that is also the frequency or called HZ or cycles per second. A Fluke meter with HZ measuring capability is what we use to check engine speed. I work in the backup generator field.....18 years. Big, small....Commercial, RV....Homeowner.....You name it we do it......I also repair other electrical equipment.....Miller and Lincoln welders......I am a certified tech for both companies as well as on Onan RV's and work on them all the time.......

    Motor starts can and do cause a small generator to bog down in speed. Voltage goes down.... generator breakers usually do trip under that scenario.

    One more likely scenario.....your voltage was too high for some reason on the generator......takes a while for stuff to burn up under a condition like that. Another possibilty your generators governor did not respond properly.....and engine speed went high.....the voltage regulator can only regulate so much and if your voltage went high it would burn up some things easily........most electrical items can tolerate plus or minus 10 % or even more but not for long.......

  8. #8
    Electrical Contractor Bobelectric's Avatar
    Join Date
    Feb 2009
    Location
    Eighty Four,Pa. 15330
    Posts
    26

    Default

    Quote Originally Posted by jwelectric View Post
    Should this have been a neutral problem it would have shown up long before the pump test.

    It was without a doubt the inrush of current due to the starting of the motor. To start a 1/2 horse power 120 volt motor the motor will have an inrush of about 58 amps which is far more than the small generator will deliver.
    When the motor started the load on the generator caused the gasoline motor to load and speed up which in turn caused a voltage drop followed by a surge in voltage that the transformer could not handle.

    Once again, these small generators were not designed to be connected to a house load. The proper way to use one is with the use of cords plugged directly into the devices (receptacles) on the generator.

    On a side note, I have two small generators. I have horses that need water during an extended power outage (24 hours or more). I use the 7500 watt generator to power the well pump for water at the barn. The other generator is used for emergency lighting at the house. This lighting is a table lamp plugged into a drop cord ran to the generator outside. I have no transfer switches connected to my house at all.

    A power outage is a very rare event and one in which my everyday way of living is interrupted and one which I live on a limited amount of electrical use. I do not try to watch TV or surf the internet during these times.

    Should I for some reason or another need more than a cord during a power outage I will purchase a generator big enough to handle the load. What I wouldn’t do is try to haul 17 ton of rocks on a half ton pickup truck or use a portable generator to power my house. Think of it this way and see if it doesn’t make a little more sense than just saying I have a generator and I want to power up this and that during a power outage.
    We lost electrical serviice for 8 days. ran on genny 24/7.
    Winter of 2010.

  9. #9
    Electrician frenchelectrican's Avatar
    Join Date
    Jun 2007
    Location
    NE Wis / Paris France { In France now }
    Posts
    46

    Default

    Quote Originally Posted by Bobelectric View Post
    We lost electrical serviice for 8 days. ran on genny 24/7.
    Winter of 2010.
    I have lost service due from wind storm almost 20 years back and ran the diesel generators 24/7 for over 2 weeks nonstop and I do get power outage from time to time. most useally a day the most.

    Merci.
    Marc

  10. #10
    DIY Junior Member david_griffin's Avatar
    Join Date
    Feb 2011
    Location
    Denver, CO
    Posts
    25

    Default

    Quote Originally Posted by Igor View Post
    My guess is that the neutral and one of the hots were swapped somewhere, so those 120V transformers were getting 240V.
    This is also my point of view. Surges from generator, even strong, would not kill primary windings of transformers so quickly.
    It must be hot neutral swap...

  11. #11
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,226

    Default

    Should this have been a hot and neutral reversed would it not have shown up during this?
    Quote Originally Posted by krnva View Post
    2. As was stated, the thermostats for the heating systems were set down to prevent/delay/control their operation until later in the test. I do not believe that either system started up on the generator, but rather set idle. However, the refrigerator and freezer were still on the panel and may have started while I was filling the sump crock. Don't know for sure either way. Otherwise, just general lighting and outlet circuits.

  12. #12
    DIY Junior Member randolph56's Avatar
    Join Date
    Feb 2011
    Location
    NYS
    Posts
    5

    Default

    A few weeks ago I had a service call to a house where the woman had some lightbulbs blow up some only dim her surge strips melt and her fluoresant ballests burn up. In her case the neutral wire(old aluimium seu) disintagrated and could not carry the load of the furnace, refig, etc motor load starting. This sent 120v back thru the neutral and with no place to go, back thru the via the neutral to the circuits on the other phase p putting 240v across phase to neut. Took a while to find it because the disintagrated cable was hinden bey the outer jacket. I would check you gen set cord to make sure that it is made up proporly, as even from the factory it could be bad or mis connected neutral. I would also check the gen set itself with a meter and a high watt electric heater testing each outlet to make sure your gen output doesn't scew up under load.

  13. #13
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,226

    Default

    When the neutral becomes open on a 240 volt single phase circuit such as the one supplying our homes the home becomes a 240 volt series circuit. The neutral conductor on our homes will always have a voltage potential between it and an ungrounded conductor of 120 volts but it is impossible to have a potential of 240 volts between the neutral and any of the two ungrounded conductors unless there is a direct short between one of the ungrounded conductors and the neutral in which case all hell breaks loose.

  14. #14
    DIY Senior Member Rich B's Avatar
    Join Date
    Sep 2008
    Location
    New Jersey
    Posts
    259

    Default

    Quote Originally Posted by randolph56 View Post
    A few weeks ago I had a service call to a house where the woman had some lightbulbs blow up some only dim her surge strips melt and her fluoresant ballests burn up. In her case the neutral wire(old aluimium seu) disintagrated and could not carry the load of the furnace, refig, etc motor load starting. This sent 120v back thru the neutral and with no place to go, back thru the via the neutral to the circuits on the other phase p putting 240v across phase to neut. Took a while to find it because the disintagrated cable was hinden bey the outer jacket. I would check you gen set cord to make sure that it is made up proporly, as even from the factory it could be bad or mis connected neutral. I would also check the gen set itself with a meter and a high watt electric heater testing each outlet to make sure your gen output doesn't scew up under load.

    So your saying an open service neutral conductor caused higher than normal voltage to be supplied to various 120 volt circuits........and your saying this higher than normal voltage was actually 240 volts and it was caused by the open neutral.......Very interseting. Are you an electrician? If you are...I am "shocked".......LOL

    Please refer to JW's post....He expalins it a little differently than I would but I agree with him 100%

  15. #15
    DIY Junior Member krnva's Avatar
    Join Date
    Feb 2011
    Location
    VA
    Posts
    3

    Default

    So, what ever happened:

    I finally got around to getting an electrician out to check out the house/ats panel wiring and functionality and here is what he found . . .

    I appears that when the generator sits idle, everything appears to be normal, and when you plug into the 120v outlets on the side of the generator all is well, but when you connect to the L14-30 outlet on the generator and put a load on one of the 120v legs of that (L14-30) outlet, the generator circuitry responds to the load with a 251v output to that (120v) leg and no voltage to the outher (120v) leg, which was measured on each alternate 120v outlet on the generator side, as well as each row of breakers in the emergency panel in my house, so the anomaly is with the generator.

    So, I contacted the customer support number on the side of the generator (the unit is a North Shore Power Systems brand) and spoke with Honeywell customer support. I was initially told to take the unit to an authorized service center for confirmation of the problem and repair, and if the system was defective, I could file a claim for reimbursement of my costs for repairs required to my HVAC systems and other equipment. While I was talking to the repair center, I got a voicemail back indicating that because my unit was a North Shore Power Systems (rather than Honeywell) unit and that they were out of business, that I needed to contact the reseller (Costco) for assistance and return/replacement of the unit. Costco says I can return the unit, after I drain the gasoline from it, but I am guessing I will not be able to get them to cover the costs of the repairs and the electrician, so I will probably get the generator problem fixed, but I will have spent probably double the cost of the generator in repairs and troubleshooting. Timing is everything . . . no company remains to honor the warranty and back their product, but fortunately the reseller does have a satisfaction/return policy.

    Thanks to all who offered input. It appears that all were right . . . I did have a voltage problem (240 volts getting to my 120 volt stuff), and it was the generator (energizing the 120 volt leg with 240 volts). At least now, I can replace the generator and try to regain confidence in the emergency power system for my house, as well as stay warm.

Similar Threads

  1. Replies: 17
    Last Post: 01-24-2011, 08:44 AM
  2. Help interpretting test results
    By PaJohn in forum Water Softener Forum, problems, installation and reviews
    Replies: 6
    Last Post: 09-14-2010, 05:19 PM
  3. Well water test results
    By WV Hillbilly in forum Pumps and Tanks Well Forum & Blog
    Replies: 7
    Last Post: 10-03-2008, 01:10 PM
  4. Well test results and brief history
    By jeremytl in forum Pumps and Tanks Well Forum & Blog
    Replies: 4
    Last Post: 07-11-2007, 12:37 PM
  5. well test results
    By evans in forum Pumps and Tanks Well Forum & Blog
    Replies: 10
    Last Post: 12-16-2006, 06:20 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •