    Default Greenhouse ventilation motors, thermostat, and wiring

    I rent space in a greenhouse that has two ventilation fans, 1 HP motors each wired for 240V. This year one motor was bad so it was partially disconnected (one leg) and the other was turning at a much slower speed and I only got 68V across both legs at this motor. These motors are controlled by a Dayton line voltage thermostat.

    Opening up the fusebox, I could not figure out the wiring. Looked like they were wired in series with the thermostat stuck in there somewhere. I took it all apart and started over, with two legs from the fuses going to the thermostat and then on to only one fan. It now runs correctly.

    Problem is I would like to hook up the other fan but the thermostat is rated 8 amps at 240V. These motors are each ~6 amps. I know both fans used to run correctly (simultaneously) several years ago. Were they simply running 12 amps through the thermostat or could they be hooked up in a way that the thermostat could control both fans without full current going through the thermostat?

    I don't see how but figured I would ask.

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,388

    Default

    You could use the thermostat to control a power contactor...just make sure the contactor contact rating is sufficient for the motors being used. The coil of that should easily be within the range of the thermostat's ability.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    DIY Senior Member dlarrivee's Avatar
    Join Date
    Jun 2009
    Location
    Canada
    Posts
    1,172

    Default

    It would probably be just as cheap to buy a second line voltage thermostat...

  4. #4
    DIY Senior Member TJanak's Avatar
    Join Date
    Sep 2009
    Location
    South TX
    Posts
    152

    Default

    I guess they must have both been run through the thermostat, even though it would be overloaded. Two thermostats would work but it would be better if both fans turned on and off at the same time. Thanks.

  5. #5
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,624

    Default

    The description is confusing. IF the motor was bad and one leg was disconnected, why would you now try to resurrect it? A 240v thermostat should have had 4 terminals, but you imply it only had one line going through it. What was connected in series? The motors? If so, disconnecting the wire from one of them should also have also kept the other one from working until it was rewired.

Similar Threads

  1. thermostat--wiring
    By danl02026 in forum HVAC Heating & Cooling
    Replies: 3
    Last Post: 12-27-2009, 07:14 AM
  2. Thermostat wiring question
    By RickM in forum HVAC Heating & Cooling
    Replies: 1
    Last Post: 12-14-2009, 09:42 PM
  3. Wiring new thermostat to the furnace
    By keano016 in forum Boiler Forum
    Replies: 12
    Last Post: 11-16-2009, 06:34 PM
  4. Help with Thermostat wiring
    By Recked in forum HVAC Heating & Cooling
    Replies: 0
    Last Post: 03-27-2009, 03:25 PM
  5. Upper Thermostat wiring
    By erikthewarm in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 03-07-2005, 07:21 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •