    Default Oil Furnace - intermittent problem

    For starters I have a forced hot air system w/ a Beckett oil burner, and tjernlund power venter.

    Over the past couple months the furnace occasionally will not turn on when the digital programmable thermostat calls for heat. The ignitor reset button needs to be pushed to restart the furnace, the furnace will ignite on the first try and stay runnig w/o any issues for a few days.
    The problem usually occurs during the day...when I leave for work (6:30 AM) the programmable thermostat is set to 60 degrees, the furnace is set to kick on at 4:00 PM when the thermostat is set to 68degrees.
    A few times a week, when I get home from work the house has not been warmed to the set 68 degrees. The furnance typically doesn't need to run during the day because the temperature in the house does not drop to 60 degrees.

    I've had the furnace cleaned and serviced, and the technian could not find any problems. I replaced the Honeywell ignitor w/ a new one. I also cleaned the "air sensor tube" that is located on the power venter with compressed air. Neither of these "repairs" solved the problem.

    This problem started about 2 weeks after I did a bathroom remodel where there was a lot of dust..not sure if this could be a contributing factor. I replaced the air filter, after I completed the work.

    Thanks for any assistance.
    Last edited by Dirk-D; 02-25-2011 at 08:44 AM. Reason: missing info

  2. #2
    DIY Junior Member david_griffin's Avatar
    Join Date
    Feb 2011
    Location
    Denver, CO
    Posts
    25

    Default

    Bathroom remodeling may be irrelevant or a coincidence.
    Some things I would check:

    1. electrodes this is the main cause of misfire. Maybe they are too far or too close to the nozzle.
    2. You should buy pressure gauge and vacuum gauge and you should measure oil pressure during operation. You will find a box for oil serviceman on "the biggest auction service" with all hoses and everything you need.
    Serch for
    "oil burner pressure"
    "oil burner gauges"

    3. Check the photo resistor whether it operates properly.

    4. maybe air/fuel mixture is not proper. Search auctions for "combustion analyzer" maybe you find something cheap.

    5. It can be caused by any factor... you have to eliminate one by one.

    Believe me it is not so hard.

    In general you have to download PDF manual for your burner and you should read it.
    Last edited by david_griffin; 03-08-2011 at 02:37 PM.

  3. #3
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,191
    Blog Entries
    1

    Default

    I also cleaned the "air sensor tube" that is located on the power venter with compressed air.
    I looked at a furnace the other day that had the connector for the vacuum hose blocked. I was able to clear the fitting with a small drill bit.

  4. #4
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,935

    Default

    Draft has to be proved before power is sent to the primary control so... It's not the power venter. From there though it could be any one of about 20 different things, however that the problem usually occurs after the unit has cooled down I have to suspect there is a problem with ignition and or the nozzle. Low voltage may be another issue too.

  5. #5
    DIY Junior Member david_griffin's Avatar
    Join Date
    Feb 2011
    Location
    Denver, CO
    Posts
    25

    Default

    Yes, 80% it is ignition problem. Electrodes, voltage from transformer. Take out this burner and try to observe ignition electrodes without fuel.

Similar Threads

  1. Intermittent Flush Problem
    By DrK in forum Toilet Forum discussions
    Replies: 0
    Last Post: 12-03-2010, 09:24 AM
  2. intermittent problem with guest bathroom toilet finally shows up
    By Thatguy in forum Toilet Forum discussions
    Replies: 5
    Last Post: 11-21-2010, 07:37 AM
  3. Random Intermittent Toilet Flush Problem
    By Mark M in forum Toilet Forum discussions
    Replies: 17
    Last Post: 02-05-2007, 01:54 AM
  4. incomplete flush in all our toilets - intermittent problem
    By kara in forum Toilet Forum discussions
    Replies: 6
    Last Post: 05-12-2006, 06:32 AM
  5. Intermittent Hot Water Problem
    By esteve999 in forum Shower & bathtub Forum & Blog
    Replies: 0
    Last Post: 11-30-2004, 07:23 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •