    Default Going To Toss The Sidearm And Install An Electric Tank

    I don't use my boiler for anything but heating hot water anyways and the sidearm tank just died. While expensive here in NY State it seems to make more sense to just put in an electric tank and install it upstairs where it is warm rather than the cold basement.

    How many kilowatts does a family of 3 usually use with a shower a day each and no one being a shower hog? Nobody showers one after the other either.

    The tank we currently have is a 30 gallon sidearm so I would assume a 40 gallon electric would replace it well enough. We have a 55 gallon whirlpool tub that rarely gets used but the sidearm 30 barely filled it.

    I plan on just using the Peerless boiler during the winter as a backup and draining it for the majority of the year and do all my heat as I do now with the pellet stove.
    Is there anything I am missing here?

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,412

    Default

    A boiler assisted tank can heat a lot more water than an electric. The recovery rate is higher as well, so a 40-gallon electric may not (likely won't) fill the tub. Once hot, it doesn't take all that much to keep it hot in an electric tank. A Kw=3412BTU. One BTU can raise one pound of water one degree. So, depending on how cold the water coming in is, and how hot you make it, and how much you use, you can figure it out. A gallon of water weighs about 8# (less, but that would give you some room for standby losses).

    So, to raise 40-gallons of water from say 40-degrees to 120-degrees (about the minimum you want) means:
    40*8 or 320# of water, *80 degrees, or 25600BTU /3412 = about 7.5Kwhr.

    Then, add in any other hot uses during the day, and you can figure out approximately how much energy it will take; then, multiply by the local rates. Sometimes, it is a tiered rate, and the more you use, the higher the cost/Kw, so it might bump you up to a higher rate.
    Last edited by jadnashua; 02-24-2011 at 06:05 PM.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    DIY Member drizler's Avatar
    Join Date
    Feb 2009
    Location
    New York
    Posts
    36

    Default

    Thanks for the explaination. I guess a 40 will fill the bill fine. One last thing. Any specific wiring schematics out there for one of these. I have replaced a few in my day but they were all many years between and already set up. Off hand I am assuming a 12/2 romex straight to it's own circuit at the box with no other special considerations. I am going to put this in an drain pan like no one ever does for that eventual day it leaks. Any big consideration on models / makes besides the warranty? I don't plan on getting anything magnificant as changing out an annode is no big deal to me every 5 years or so. Neither is draining and flushing.

  4. #4
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,412

    Default

    Depends on the model you purchase, but I doubt 12g would cut it. Most spec either a 30A or 40A circuit breaker (full-sized, 240vac), and you have to abide by the rules based on the load and the installation instructions of the one you get. Probably either 8g or maybe 10g, depending on the CB needed.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  5. #5
    DIY Member drizler's Avatar
    Join Date
    Feb 2009
    Location
    New York
    Posts
    36

    Default

    Oh, I didn't even know they provided instructions with electric heater. That will do for me. If there's directions I can do about anything. I just get lost on those things that are left open to interpretation, local codes ect. Thanks for the advice.

  6. #6
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Most residential WH are 4500 watts, which on 240 is about 18,75 amps. 10 gauge will be required.
    Because of slower recovery on electrics, I would consider a 50 gallon.
    Forget the whirlpool. A 50 gallon tank, if you have it set hot, about 140, will give you 35 gallons of water at bathing temp. On a good day.

  7. #7
    DIY Member tk03's Avatar
    Join Date
    Jan 2011
    Location
    Harrisburg, pa
    Posts
    56

    Default

    I agree that a 50 gallon is definitely the size required but it will never heat your whirlpool tub. The tub may become unusable due to lack of recovery. A properly piped 30 gallon indirect water heater will recover way more than a fifty gallon electric.

Similar Threads

  1. Combining an electric Tank with electric Tankless
    By Dkrasko in forum Tankless Water Heater Forum
    Replies: 15
    Last Post: 03-27-2014, 08:24 AM
  2. Combining an electric Tank with electric Tankless
    By Dkrasko in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 14
    Last Post: 11-28-2008, 03:14 PM
  3. Seperate Electric Hot Water Tank Meter
    By molo in forum Electrical Forum discussion & Blog
    Replies: 14
    Last Post: 10-13-2007, 04:36 PM
  4. need to buy an electric hot water tank
    By Danny B in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 7
    Last Post: 10-17-2006, 05:56 AM
  5. Hot Water tank - Electric
    By lybush in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 19
    Last Post: 01-08-2005, 11:34 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •