Basment Bathtub vent question

Users who are viewing this thread

jsmithv

New Member
Messages
2
Reaction score
0
Points
0
Location
Utah, USA
I am working on my basement bathroom, and very new to this stuff, but i'm stuck thinking about the venting options for the tub. I have a couple questions and I've attached a quick drawing of what I have.

1. Is the tub line already vented perhaps along with the toilet stubout, or not?
2. Can i tie the wetbar drain into the same drain as the vanity? I have the wetbar sink venting with an AAV which is permitted in my area, so I don't need to worry about venting that.
3. If the 2" line under the concrete does need its own vent, how can I tie into the 1.5" vent stack that's there? The wetbar drain line in in the 2x4 wall, so I can't go around it and up into the vent line?

Or perhaps I should drain the wetbar line and the tub both into the 2" tub drain and that will clear a path to get to the vent? Any thought would be appreciated. Thanks in advance,
AR-M450_20110224_083217%20%28Small%29.jpg
 

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
Hopefully the pipe coming out of the floor to the lav is 2", because a 1-1/2 should not be run underground.
If so, the 2" shower/tub drain and the toilet MIGHT be wet vented through the lavatory.

Finding out how is was installed is a problem. If you cannot confirm the original installation through the builder, you might have to open up the floor to see what is there.
 

jsmithv

New Member
Messages
2
Reaction score
0
Points
0
Location
Utah, USA
Yes, where it comes out of the floor it's 2"; it reduces to 1.5" at the cleanout. I should have noted that dimension on my drawing. Is there a way to test if its wet vented without digging all the concrete up? e.g. put a ptrap in the hole and pour water down? If its vented properly i would think the water would pour through without issue. If not, wouldn't I see it trying to gulp air through the ptrap and maybe smell sewer? Maybe that's a stupid question.

Maybe I'm better off just to vent the tub line anyways? The room next to this, behind the wall with the pipe in it, is my mechanical room. I guess I could just pipe through there into the vent or use an aav...:confused:
 

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
You could have a plumber run a camera down the lines to see how the connections are made, I couldn't say for sure what he might be able to see with the camera without trying it.
 