    I'd like to run power out to a shed for some lights and an outlet.

    I plan to go underground in pvc conduit with THWN conductors in it.

    Generally you'd probably use a PVC LB on the exterior of the home to change directions with, and a junction box on the inside of the home... Unfortunately I'd rather not have an access panel in a finished bathroom to keep the junction box legal.

    So instead I'd like to use a larger PVC weather tight junction box on the exterior of the home, rather than a smaller LB, that way I can splice my THWN to my NMD90 in that box rather than inside the home.

    I'm just not sure what the proper way of running 12/2 NMD90 through the exterior wall into the PVC box is... I assume I should use a PVC nipple, but what about the interior end of the nipple, do I just need a bushing of some sort?

  2. #2
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,522

    Default

    You are over the border and I think under a little different rule than us southerners.
    Down here we don’t like the idea of having NM cable outside even for a short distance. I would recommend that you use a UF cable to the junction box and don’t see anything wrong with the installation other than the cable going through the wall to be made up outside.

  3. #3

    Default

    Quote Originally Posted by dlarrivee View Post
    I'm just not sure what the proper way of running 12/2 NMD90 through the exterior wall into the PVC box is... I assume I should use a PVC nipple, but what about the interior end of the nipple, do I just need a bushing of some sort?
    Female connector or a male (with a bushing if larger than 1/2") should be fine.

    -rick

  4. #4
    DIY Senior Member dlarrivee's Avatar
    Join Date
    Jun 2009
    Location
    Canada
    Posts
    1,172

    Default

    Quote Originally Posted by jwelectric View Post
    You are over the border and I think under a little different rule than us southerners.
    Down here we don’t like the idea of having NM cable outside even for a short distance. I would recommend that you use a UF cable to the junction box and don’t see anything wrong with the installation other than the cable going through the wall to be made up outside.
    The cable itself wouldn't ever be outside, it would come into the backside of the weather-tight junction box on the exterior.

  5. #5
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,522

    Default

    Quote Originally Posted by dlarrivee View Post
    The cable itself wouldn't ever be outside, it would come into the backside of the weather-tight junction box on the exterior.


    Help me out here, please. Is the word "exterior" you use above meaning outside?

  6. #6
    DIY Senior Member dlarrivee's Avatar
    Join Date
    Jun 2009
    Location
    Canada
    Posts
    1,172

    Default

    I found this on Google Image Search:


    Whoever installed this junction box, simply drilled a hole in the back of the box... I'd rather have a pvc connector that would at least reach through the sheathing... Or am I creating more work for myself?
    Last edited by dlarrivee; 02-20-2011 at 03:39 PM.

  7. #7
    Electrical Contractor Jim Port's Avatar
    Join Date
    Aug 2009
    Location
    Maryland
    Posts
    156

    Default

    Except for the lack of a connector into the back of that box this is a commonly accepted trade practice.

  8. #8
    DIY Senior Member dlarrivee's Avatar
    Join Date
    Jun 2009
    Location
    Canada
    Posts
    1,172

    Default

    Quote Originally Posted by Jim Port View Post
    Except for the lack of a connector into the back of that box this is a commonly accepted trade practice.
    That connector is what I wanted to clarify... I suppose almost any type of connector would "work", but I'd like to know what the best practice is whenever I do something. Is there no requirement for the connector to clamp the cable where it enters the box?

Similar Threads

  1. pex to fixture transition
    By joatmoo in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 06-14-2010, 02:15 PM
  2. Transition cement
    By ilya in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 01-11-2010, 06:29 PM
  3. PCV transition
    By Rancher in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 9
    Last Post: 01-01-2008, 12:47 PM
  4. Transition from conduit to romex.
    By remster in forum Electrical Forum discussion & Blog
    Replies: 15
    Last Post: 06-18-2007, 04:53 PM
  5. cast to pvc transition
    By buddyluv in forum Toilet Forum discussions
    Replies: 2
    Last Post: 04-08-2005, 10:08 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •