Results 1 to 5 of 5
Thread: Tamper resistant options for 2 wire supply to receptacles?
    DIY Junior Member weaver's Avatar
    Jan 2009
    NE Ohio
    Default Tamper resistant options for 2 wire supply to receptacles?
    Would like to convert to tamper resistant receptacles to protect kids in house. Existing supply is 2 wire. Have been able to find only receptacles with ground. Can’t afford to rewire existing 2 wire knob & tube with 3 wire now. Would prefer not to tear up brick & plaster lath & floors to supply ground to each location (4 levels, 1920’s house).
    Can I use the 3 hole TR receptacles? Would labeling them “No Ground” and / or blocking the ground connection to prohibit the use of a three prong plug be acceptable or advisable?
    Thanks. Bob
    Jun 2007
    North Carolina
    250.130 (C) Nongrounding Receptacle Replacement or Branch
    Circuit Extensions. The equipment grounding conductor
    of a grounding-type receptacle or a branch-circuit extension
    shall be permitted to be connected to any of the following:
    (1) Any accessible point on the grounding electrode system
    as described in 250.50
    (2) Any accessible point on the grounding electrode conductor
    (3) The equipment grounding terminal bar within the enclosure
    where the branch circuit for the receptacle or
    branch circuit originates
    (4) For grounded systems, the grounded service conductor
    within the service equipment enclosure
    (5) For ungrounded systems, the grounding terminal bar
    406.3 (D) Replacements. Replacement of receptacles shall comply
    with 406.3(D)(1), (D)(2), and (D)(3) as applicable.
    (1) Grounding-Type Receptacles. Where a grounding
    means exists in the receptacle enclosure or an equipment
    grounding conductor is installed in accordance with
    250.130(C), grounding-type receptacles shall be used and
    shall be connected to the equipment grounding conductor in
    accordance with 406.3(C) or 250.130(C).
    (2) Ground-Fault Circuit Interrupters. Ground-fault
    circuit-interrupter protected receptacles shall be provided
    where replacements are made at receptacle outlets that are
    required to be so protected elsewhere in this Code.
    (3) Non–Grounding-Type Receptacles. Where attachment
    to an equipment grounding conductor does not exist
    in the receptacle enclosure, the installation shall comply
    with (D)(3)(a), (D)(3)(b), or (D)(3)(c).
    (a) A non–grounding-type receptacle(s) shall be permitted
    to be replaced with another non–grounding-type receptacle(
    s).
    (b) A non–grounding-type receptacle(s) shall be permitted
    to be replaced with a ground-fault circuit interruptertype
    of receptacle(s). These receptacles shall be marked
    “No Equipment Ground.” An equipment grounding conductor
    shall not be connected from the ground-fault circuitinterrupter-
    type receptacle to any outlet supplied from the
    ground-fault circuit-interrupter receptacle.
    (c) A non–grounding-type receptacle(s) shall be permitted
    to be replaced with a grounding-type receptacle(s)
    where supplied through a ground-fault circuit interrupter.
    Grounding-type receptacles supplied through the groundfault
    circuit interrupter shall be marked “GFCI Protected”
    and “No Equipment Ground.” An equipment grounding
    conductor shall not be connected between the groundingtype
    receptacles.
    Jan 2009
    NE Ohio
    Thanks jwelectric. Very helpful. Makes sense. Can I assume that 2011 code doesn't change this? Thanks again. Bob
    Jun 2007
    North Carolina
    If you are under the 2011 then the replacement of a two wire will require that it be both GFCI and Arc Fault protected after 1-1-14
    Jan 2009
    NE Ohio
    jwelectric: Another layer of thanks. Bob
  1. Tamper resistant receptacles - remodeling project
    By chuck b in forum Electrical Forum discussion & Blog
    Last Post: 01-31-2011, 12:16 PM
  2. toilet supply makeover options...
    By roadk in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Last Post: 11-27-2009, 07:05 AM
  3. Any Tamper Resistant Tank Lids for Toto?
    By Firemark in forum Toilet Forum discussions
    Last Post: 08-25-2009, 12:59 PM
  4. options for moving toilet water supply
    By DanMc in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Last Post: 01-09-2009, 07:28 PM
  5. code compliance - GFCI and tamper resistant
    By beekerc in forum Electrical Forum discussion & Blog
    Last Post: 10-23-2008, 03:18 PM