    Good morning all. Don't know if this is the right forum but here goes. I want to replace my current 40 gal NG water heater with a power vent model.(AO Smith GPVD40?) The current heater is next to the boiler sharing the flue and about 40' from where I need the hot water. I want to move the WH over to the other side of the house right below the kitchen and 2nd floor bath and vent it thru the foundation. There is a 3/4 gas line that supplies my stove about 5' from where I'm going to move the WH to. The current 1 shares an 1 1/4" feed that breaks down to 2- 3/4" drops, 1 to the WH and 1 to the boiler (both are further reduced to 1/2"). Finally, the question. Does the 3/4" that feeds my stove have enough volume to also feed the WH. or should I increase the size to 1" or 1 1/4"? Any feedback would be appreciated. Thanks

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,405
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    Sounds fine to me unless its huge range with a grill and 12 kids at home. Try it, cant hurt anything.

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,653

    Default

    Recommended gas lines sizes depend on several computations none of which you have given us.

  5. #5
    DIY Junior Member randolph56's Avatar
    Join Date
    Feb 2011
    Location
    NYS
    Posts
    5

    Cool gas size

    Thanks for the replies. After I posted and then did some more searching I realized that I didn't give enough info. From the link I figured what cfh was needed and the capacity/volume of 3/4 with the length and # of 90's etc. So, yes in my case 3/4 will handle what I need, but just to be sure, I called the utility. Thanks again.

    Last edited by Terry; 04-29-2011 at 06:22 PM.

Similar Threads

  1. Pipe size for pipe to water tank.
    By odysseus99 in forum Pumps and Tanks Well Forum & Blog
    Replies: 1
    Last Post: 02-02-2011, 12:12 PM
  2. Pump Size, Pipe Size, CSV location????
    By fausdick in forum Pumps and Tanks Well Forum & Blog
    Replies: 6
    Last Post: 01-20-2009, 05:40 AM
  3. Pipe size
    By Yersmay in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 02-14-2006, 10:14 AM
  4. what pipe size with 5/8" meter, to replace old pipe?
    By sbaitso in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 7
    Last Post: 01-05-2006, 07:18 AM
  5. What size pipe can I put through a 2x4
    By pmccurdy in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 8
    Last Post: 07-21-2005, 05:28 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •