    Default Oil Boiler Overheating

    My boiler is set to the aquastat all the way down to 140 and the burner will fire until 200 is reached then shut off after the relief valve shoots out steam and water. I am not sure if it does this because there is a limit, but seems like the connection from my thermostat to the boiler isn't working. Thermostat is wired properly, but when I set the thermostat to 15C, it goes up to 20C at times, can anyone help? I have a technician coming in during the week but is cold and would like to see if i can fix this. I have heat just have to manual shut down the power to the boiler because it reaches 200 which throws the relief valve open. With the high and low points on the relay set to the lowest, why is it going to 200? wiring problem? I can manually turn on the power and run the burner until 160 and shut it down but the curc pump will not run as well. The boil was to heat a small apartment building maybe 8 units, would i have to replace the nozzle to a lower btu nozzle?
    Last edited by soaddrummer; 01-16-2011 at 01:00 PM.

  2. #2
    DIY Junior Member soaddrummer's Avatar
    Join Date
    Jan 2011
    Location
    CAN
    Posts
    2

    Default

    The boiler i am using is a Clare HMT with water heater coil which is removed, would the wiring to the aquasat need to be modified without the coil possibly?

  3. #3
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,937

    Default

    If your high limit is set at 140 and the burner continues to fire past that setting then the aquastat is bad or the thermocouple is not fully seated in the aquastat well

  4. #4
    DIY Junior Member dapoppa's Avatar
    Join Date
    Jul 2010
    Location
    NJ
    Posts
    9

    Default

    As Tom said or an accumulation of mud or crud on the outside of the well restrcting heat transfer.

  5. #5
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,390

    Default

    Many boilers rely on a well into the water where a sensor is installed. The sensor stays dry, but it must be fully inserted. It might be somethings (as already noted) as the sensor (aquastat) is not seated all the way in, and is thus sensing air temp, rather than the water temp. It could be bad as well. Testing the sensor can usually be done with a multimeter and the spec sheet. The resistance across it will vary based on the temperature.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

Similar Threads

  1. Water Heater overheating and tripping breaker?
    By towthis2002 in forum Water Heater Forum, Tanks
    Replies: 7
    Last Post: 01-21-2010, 06:15 AM
  2. pump motor overheating fast
    By Randall59 in forum Pumps and Tanks Well Forum & Blog
    Replies: 10
    Last Post: 08-07-2009, 05:11 AM
  3. Motor overheating - now what?
    By JohnnyMalaria in forum Pumps and Tanks Well Forum & Blog
    Replies: 13
    Last Post: 01-06-2009, 03:57 PM
  4. Overheating boiler
    By JuanValdes in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 11-05-2007, 12:26 PM
  5. How to avoid overheating rough-in valves.
    By Carl in Redwoods in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 05-22-2007, 07:21 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •