    What type of tank to use,
    This is what I have, a steel hydropneumatic galvanize tank of 525 gal;.that starting to leak. A 220/240 3 phase eletric system
    The well is 120 feet deep, 8" casing, 2 inch pipe, about 95 gpm," 5 HP " sumersible goulds pump.
    The residence has only a mother, 7 children, two bathrooms, sink, john, shower in both, kitchen sink, washing machine,"everyday use", one out door spicket, and lawn.

    In order to save this family money on both the replacement and the cost of electric would it be better to change to a bladder or diafram tank, steel, or fiberglass tanks.
    If the change would be to the bladder tanks, would the bleed off valve 10 feet down the well have to be plugged?

  2. #2
    In the Trades Texas Wellman's Avatar
    Join Date
    Feb 2010
    Location
    SE Texas-Coastal
    Posts
    487

    Default

    Sounds like an irrigation well got turned into residential.

    I would think that instead of replacing that big of a tank with another big tank it would be more economical to install a smaller HP sub pump like a .5 or 1 HP 10 gallon per minute pump. Then add a 10-20 gallon draw-down bladder tank. Of course you would have to have the means to pull the 5 horsepower pump, probably set on 2" galv. pipe.

    I'm sure valveman will chime in here but I think a CSV (cycle stop valve) can be used to throttle the output of the pump back but it will be expensive. You will probably end up spending almost as much for the CSV and new tank as you would replacing the old pump with a new smaller pump and new smaller tank....

  3. #3
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,685

    Default

    Quote Originally Posted by Rekrap View Post
    If the change would be to the bladder tanks, would the bleed off valve 10 feet down the well have to be plugged?
    With a bladder or diaphram, there would be no air volume control so yes, you would want to get rid of the bleeder.

  4. #4
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,156

    Default

    If you are not going to need the 95 GPM for irrigation or something else, then I agree with TW that changing to a smaller pump would be a good idea. The smaller pump can use a smaller 44 gallon tank ($300). Or it can even be as small as 4.4 gallon size tank ($75) if used with a CSV ($200).

    However, buying a new pump now ($1,000?) will be more expensive than just replacing the tank. And yes if you switch to bladder tanks you may need to remove the bleeder orifice as Lligetfa suggested.

    If you never use more than 25 GPM, which I doubt, you can use a CSV1Z with a 3 GPM minimum for the 5 HP pump. You may still need to remove the bleeder but, with the CSV you can replace the big tank with as small as a 44 gallon size tank. CSV ($200) and a 44 gallon tank ($300).

    If you remove the above ground check valve while installing the 44 gallon tank and CSV, the bleeder in the well should stay closed and may not have to be removed. If it is a rubber bleeder, the back pressure from the CSV may pop it out, then you will have to lift the pump and plug the hole (service call $?). If it is a brass bleeder and is still good, you should not have to pull the pump up to plug anything (no service call $0). But you won’t know until you try it.

    In this way the tank and CSV will also work with a smaller pump, when the time comes to replace the 5 HP.

    CSV’s are not expensive. Even if you want to still be able to use the 95 GPM, you would only need a 2” CSV ($900) and a single 80 gallon bladder tank ($500). Some people might think the 2” CSV is expensive at $900, but without it you would need at least four 80 gallon pressure tanks ($2,000), or three 119 gallon bladder tanks ($2400), or replace the 525 galv tank ($3,000?). Even then all those big tanks will not do as good a job as the CSV and one tank.

    No matter the size of CSV needed, it always more than offsets its cost by using a much smaller pressure tank. There are other benefits to the CSV as well, like variable flow rates, eliminating water hammer, delivering constant pressure, and eliminating cycling, which makes the pump last much longer.

    To see how the CSV works see this link.
    http://www.cyclestopvalves.com/index2.html

  5. #5
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,685

    Default

    Quote Originally Posted by valveman View Post
    ...And yes if you switch to bladder tanks you may need to remove the bleeder orifice as Lligetfa suggested.

    If you never use more than 25 GPM, which I doubt, you can use a CSV1Z with a 3 GPM minimum for the 5 HP pump. You may still need to remove the bleeder but, with the CSV you can replace the big tank with as small as a 44 gallon size tank. CSV ($200) and a 44 gallon tank ($300).
    If you went with the CSV and choose a tank with an air volume control instead of a bladder or diaphram type, you could keep the existing snifter/bleeder/checkvalve if pulling up the pump and redoing the plumbing to remove it is cost prohibitive.

  6. #6
    DIY Junior Member Rekrap's Avatar
    Join Date
    Feb 2011
    Location
    bernardino, CA
    Posts
    3

    Thumbs up Best replacement for well tank

    Texas Wellman
    Liligrtfa
    Valveman/

    Gentlemen;
    You hit the nail on the head with, "Sounds like an irrigation well turned into residential.

    My daughters husband went to Heaven (I think) several years ago, and now there is no need for the irrigation.

    She cannot afford to do that anymore, I am pushing 85 down the line, but thanks to God I am still able to do what needed to be done for her.
    I have no problem in pulling the pump ( but would rather not) and remove the old galvanized steel tank out of the pump house with a replacement.

    So with all your information I have to make up my mind as to just which way to go.

    What I should have mention was that the present pump and rubber bleed off valve was replaced two years ago, so I feel that is is still fairly new.
    The 2" pipe from the pump was replaced 7 years ago with plastic? / PVC? well pipe.

    Lligetfa, mention the air volume tank, is that the same as the one I have at present ?but a smaller size with the CSV, is so, what size tank would you recomend
    Many many thanks to y'al

  7. #7
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,685

    Default

    Quote Originally Posted by Rekrap View Post
    What I should have mention was that the present pump and rubber bleed off valve was replaced two years ago
    Quote Originally Posted by valveman View Post
    If it is a rubber bleeder, the back pressure from the CSV may pop it out, then you will have to lift the pump and plug the hole
    I assume there is a snifter valve to go with the bleeder.

    Based on valveman's advice, the rubber bleeder would not withstand the higher hold-back pressure the CSV would exert on it. If you keep the bleeder you will need a large tank with air volume control to reduce cycling. Your existing tank would, in all likelyhood have an air volume control to vent off the air drawn into the line by the snifter/bleeder setup. Bladder/diaphram precharge tanks don't require a snifter to introduce air.

    The other purpose for a snifter/bleeder is to drain down the line to prevent freezing if lines are not buried deep enough.

  8. #8
    In the Trades Texas Wellman's Avatar
    Join Date
    Feb 2010
    Location
    SE Texas-Coastal
    Posts
    487

    Default

    Based on what you've told me I believe that the best thing is to replace the 5-HP with a much more suited .5 - 1 HP submersible pump. No matter what you try you are still going to have to deal with that beast of a pump doing a job it's not designed for. even with a 500 gallon tank I don't think that pump could run long enough to keep it from cycling and starting that beast has got to pad the electric bill somewhat.

    Since you're galv. tank is already leaking I would definitely go with a good bladder tank and keep the metal connections down to a minimum and try to use all pvc or non-metallic fittings unless it's brass or stainless.

    Have you gotten any bids or do you plan to do the work yourself? Be careful, without the proper equipment things could get ugly in a hurry. Using a back-hoe or front end loader to pull a well can be a tricky proposition at best.


    Quote Originally Posted by Rekrap View Post
    Texas Wellman
    Liligrtfa
    Valveman/

    Gentlemen;
    You hit the nail on the head with, "Sounds like an irrigation well turned into residential.

    My daughters husband went to Heaven (I think) several years ago, and now there is no need for the irrigation.

    She cannot afford to do that anymore, I am pushing 85 down the line, but thanks to God I am still able to do what needed to be done for her.
    I have no problem in pulling the pump ( but would rather not) and remove the old galvanized steel tank out of the pump house with a replacement.

    So with all your information I have to make up my mind as to just which way to go.

    What I should have mention was that the present pump and rubber bleed off valve was replaced two years ago, so I feel that is is still fairly new.
    The 2" pipe from the pump was replaced 7 years ago with plastic? / PVC? well pipe.

    Lligetfa, mention the air volume tank, is that the same as the one I have at present ?but a smaller size with the CSV, is so, what size tank would you recomend
    Many many thanks to y'al

  9. #9
    Well Drilling/Service justwater's Avatar
    Join Date
    May 2010
    Location
    NE FL, SE GA
    Posts
    320

    Default

    Quote Originally Posted by Texas Wellman View Post
    Have you gotten any bids or do you plan to do the work yourself? Be careful, without the proper equipment things could get ugly in a hurry. Using a back-hoe or front end loader to pull a well can be a tricky proposition at best.
    especially if it is actually installed with pvc pipe. you can manhandle steel with chains and whatever and pull it up a couple feet at a time, but if its pvc.. you cant handle it the same way. it will definitely be lighter, probably not light enough to attempt by hand. if you couldnt pull 20' of pipe in one shot with something, i wouldnt attempt it. last thing u want it to break the pvc and that big boy fall to the bottom..
    Last edited by justwater; 02-16-2011 at 07:29 AM.

  10. #10
    That's all folks! Gary Slusser's Avatar
    Join Date
    Aug 2004
    Location
    Wherever I park the motorhome.
    Posts
    6,790

    Default

    A pipe vise does the job.

    http://www.campbellmfg.com/catalog/r05.htm
    Gary Slusser Retired (= out of business)
    Click Here to learn how to correctly size or program a water softener.
    CAUTION, as of Nov 12 2013 all YouTube videos showing how to rebuild a Clack valve have an error in them that can cause damage.

  11. #11
    Well Drilling/Service justwater's Avatar
    Join Date
    May 2010
    Location
    NE FL, SE GA
    Posts
    320

    Default

    yep, GS is right. they make a tool for any job. not sure how much they would charge for one, but anything is available for a price, and you still have to pull it up.. i'd guess by the time you bought all the "proper" tools to get it out safely, you coulda been done paid someone or traded the work for the pipe and pump.. then u could install the new. id hate so hear something happened and u dropped a 5hp pump down a well.. on pvc, which would make it 5 times harder to fish. but this is a DIY site.. and its not impossible.

  12. #12
    That's all folks! Gary Slusser's Avatar
    Join Date
    Aug 2004
    Location
    Wherever I park the motorhome.
    Posts
    6,790

    Default

    Quote Originally Posted by justwater View Post
    yep, GS is right. they make a tool for any job. not sure how much they would charge for one, but anything is available for a price, and you still have to pull it up.. i'd guess by the time you bought all the "proper" tools to get it out safely, you coulda been done paid someone or traded the work for the pipe and pump.. then u could install the new. id hate so hear something happened and u dropped a 5hp pump down a well.. on pvc, which would make it 5 times harder to fish. but this is a DIY site.. and its not impossible.
    Replacing this 5 hp pump is the right thing to do all around.

    Since the pump and PVC are only 2 years old, I suspect he could sell the pump, PVC and probably the cable fairly easily and use some of the money (he could post it on the BB in the local pump/plumbing supply houses and weekly/monthly Penny Saver paper/Craig's list etc. free of charge) for the pipe vice to get it out of the well and the new 2 wire 1/2 hp 10-13 gpm pump needed for a 2 bathroom house and some 12/3 flat ribbon cable and a roll of PE pipe and a couple fittings and hose clamps (all bought online) and a new 'bladder' type pressure tank and give his daughter the rest of the money.

    He sounds handy and I bet he can figure out how to get this pump out of the well. Since it is only 2 yrs old, I wouldn't trade it to someone just for pulling it.
    Gary Slusser Retired (= out of business)
    Click Here to learn how to correctly size or program a water softener.
    CAUTION, as of Nov 12 2013 all YouTube videos showing how to rebuild a Clack valve have an error in them that can cause damage.

  13. #13
    Well Drilling/Service justwater's Avatar
    Join Date
    May 2010
    Location
    NE FL, SE GA
    Posts
    320

    Default

    all around best choice is getting it out and replacing with proper size, i wont argue that. i missed that the pump was only 2yrs old.. i dunno, itd be his call.. i think i'm with u, i wouldnt wanna trade equipment that new just to get it out.. but some might. before i did anything, i might contact the guy that put it in and see if he'd be willing to work some kind of deal. and OP does sound like a handy fella, and can probably find a way to get it out.. maybe even without the vice. if he chooses to tackle it, i just hope he takes his time and is careful.

  14. #14
    That's all folks! Gary Slusser's Avatar
    Join Date
    Aug 2004
    Location
    Wherever I park the motorhome.
    Posts
    6,790

    Default

    So give him some hints on how to do it. I've seen guys on here that built tripods, used backhoes etc.. What he needs is a way to grip the PVC so he doesn't drop or damage it while undoing the couplers.
    Gary Slusser Retired (= out of business)
    Click Here to learn how to correctly size or program a water softener.
    CAUTION, as of Nov 12 2013 all YouTube videos showing how to rebuild a Clack valve have an error in them that can cause damage.

  15. #15
    Well Drilling/Service justwater's Avatar
    Join Date
    May 2010
    Location
    NE FL, SE GA
    Posts
    320

    Angry

    why do I gotta give hints? I've never even heard of a 5hp hung on 2" PVC.

    u dont need to grip the pipe if u are planning on "undoing" it at the couplers. ud just build a pair of homemade elevators (notched blocks of wood, torch-notched steel plate, etc) and pull it out in 20' sections, resting and securing each coupler on an elevator. it's on him to brainstorm and find out how he could pull 20' joints up with whatever material or equipment he has access to. i already said this would be the only way i would attempt it. anything beyond that,.. u give him some hints.

    somebody smarter than me do some math and figure out about how much this would weigh. 5hp pump on 120' 2" PVC .. full of water.

Similar Threads

  1. Oil Tank Replacement
    By Massjim in forum HVAC Heating & Cooling
    Replies: 13
    Last Post: 09-05-2009, 03:08 AM
  2. Oil Tank Replacement Part II Should I go Gas?
    By Massjim in forum HVAC Heating & Cooling
    Replies: 5
    Last Post: 07-22-2009, 10:05 AM
  3. Well Storage Tank replacement
    By mrmichaeljmoore in forum Pumps and Tanks Well Forum & Blog
    Replies: 58
    Last Post: 04-06-2009, 08:04 AM
  4. pressure tank replacement
    By lakecat in forum Pumps and Tanks Well Forum & Blog
    Replies: 1
    Last Post: 12-29-2007, 09:24 AM
  5. Pressure Tank Replacement
    By rhineg57 in forum Pumps and Tanks Well Forum & Blog
    Replies: 2
    Last Post: 07-19-2005, 05:50 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •