    Default pulling 8-3 romex

    hello everyone i need to pull a 8-3 romes through a 3/4 inch gass pipe and go past 2 90 degree angles the pull is only 12 to 15 feet long is this possible

  2. #2
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    You CANNOT pull NM cable through gas pipe. In fact, if the 90 deg angles you mention are typical gas fittings, it would literally be impossible.

    WHY do you need to do this? Describe the installation a little better.

  3. #3
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Is this pipe also going to have gas in it?? 8-3 would significantly reduce the flow of gas....EVEN IF you could figure some way to get the wire in and out of the pipe! But if this is just conduit, you can NOT pull through 90's . Won/t happen! And why are you pulling romex through pipe....I think there are rules against that@!

  4. #4
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,151

    Default

    You can only install in UL listed conduit.
    Romex is not normally installed inside conduit anyway so I think we should hear the rest of the story.

  5. #5
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    326

    Default

    Quote Originally Posted by erniekosar View Post
    hello everyone i need to pull a 8-3 romes through a 3/4 inch gass pipe and go past 2 90 degree angles the pull is only 12 to 15 feet long is this possible
    Quote Originally Posted by Speedy Petey View Post
    You CANNOT pull NM cable through gas pipe. In fact, if the 90 deg angles you mention are typical gas fittings, it would literally be impossible.
    But it would be a lot of fun to set up a couple of lawn chairs and a large pitcher of Margaritas and watch.

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default

    PLus see the "Monster truck" they would have to attach to the wire. IF they could get a "pull' cable past the elbows, (which would be an impossibility in any case), by the time they got the wire pulled through it, the elbows would be straightened out and the gas line would be a straight section of piping.

  7. #7
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    Just as a moot point, A guy could possibly do it by blowing a small line through, or several, and then pulling multiple strands of 18 gauge wire to amount to the ampacity of the 8 gauge. Do not do it: you will die, and yonkers will burn down. Just an option on the monster truck pull. Surgical method.

    Or he could pull 16 gauge wire and buy a step up and down transformer for a few thousand bucks and run it at 600 volts.

    Hate to be the home inspector on that one.
    Last edited by ballvalve; 02-14-2011 at 10:54 AM.

  8. #8
    DIY Junior Member erniekosar's Avatar
    Join Date
    Feb 2011
    Location
    Yonkers, NY
    Posts
    5

    Lightbulb pulling 8-3 romex

    i asked if it was possible to pull 8-3 romex through 2- 90 degree angles ...... the reason is i have heavely foam insulated a new house ,and made it into a 2 family now i cannot show it as a to family with 2 kitchens i got the co already and passed all my permits but i want to run the power line for a electric stove now to make it easyer to pull it out if i need to if i get reported again the span is only 12 to 15 feet and it has 2- 90 degree angles i want to pull the 8-3 romex rite through the 3/4 inch gass pipe that is already there in the rite place that i need it mabee if the romex was heavely lubbed up i might have a chance ?/?/???/ remember there are no more inspections
    Last edited by erniekosar; 02-14-2011 at 06:28 PM.

  9. #9
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    326

    Default

    Quote Originally Posted by erniekosar View Post
    i know it is ileagal but it is possiable
    Quote Originally Posted by Speedy Petey View Post
    You CANNOT pull NM cable through gas pipe. In fact, if the 90 deg angles you mention are typical gas fittings, it would literally be impossible.
    Read this again and see if you can find your answer in there somewhere.

  10. #10
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default

    There is absolutely NO WAY you could pull any usuable size wire through gas pipe elbows, period, (an additional reason would be that there is NO fishtape that would go through them to pull the wires). IF so, they would not make "sweep" elbows for use with electrical rigid conduit.

  11. #11
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,261

    Default

    The way to put the wire in is with the Yonkers yellow pages under "electrician".

    Better yet, put in a gas stove and use the gas pipe for gas.

  12. #12
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,685

    Default

    Quote Originally Posted by ballvalve View Post
    Better yet, put in a gas stove and use the gas pipe for gas.
    That was my first thought. IMHO, gas stoves are better.

  13. #13

    Default

    I am also guessing that the electric range in question only requires a 40 amp circuit? What is the kW rating?

    You can't make that pull. That is a stupid, illegal and unsafe idea. You should not even try to make that pull but please videotape the attempt so we can all have a good laugh just in case you decide to try it.
    http://www.inspectpa.com/forum/forum.php
    My answers are based mostly on the ICC codes. Advice given is my personal opinion and every person performing work should acquire a permit from his/her jurisdiction and get the work inspected. My opinions are not directions to follow for DIYs or professionals

Similar Threads

  1. Wiring a Spa. Do I use #8 awg or 6/3 romex slimpull ?
    By nail bender in forum Electrical Forum discussion & Blog
    Replies: 63
    Last Post: 06-01-2011, 03:45 PM
  2. Installing Ceiling Fan Box and Pulling Romex
    By Kiko in forum Electrical Forum discussion & Blog
    Replies: 14
    Last Post: 06-27-2010, 12:10 PM
  3. Outlet with 10-3 Romex
    By mavisb in forum Electrical Forum discussion & Blog
    Replies: 10
    Last Post: 12-02-2009, 07:11 AM
  4. 8-3 Romex in PVC conduit
    By dabiz7 in forum Electrical Forum discussion & Blog
    Replies: 22
    Last Post: 09-26-2009, 07:44 AM
  5. AC Cable to NM (ROMEX®)
    By mrhoades in forum Electrical Forum discussion & Blog
    Replies: 7
    Last Post: 02-01-2009, 09:34 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •