These waste heat coils are used a lot where I am from, NYC, to grab the heat from hot condensate where it is not returned (district heating use). Basically you have a simple coil or tubes in the collection tank. Many companies make tank coils pre-made (all of the major heat exchanger manufacturer's do).
However, you may have a problem with the 'stuff' in your drain water. It does not sound clean to me, and if you hold it in a tank, where does all this stuff go? To the bottom of the tank? How will you get it out? Also, if you can figure out the above problem, you probably don't want to use finned tubes because they will get fouled.
I think it would be a nice test to use some 3/4" tube inside the tank and see what happens. For how much, you will need your GPM of the flow and how much Delta T you want....