Hello
Hoping to get some advise on wiring a 240v 60amp single phase oven. I have a few questions.
1) will #6 be ok with an oven pulling 53 amps?
2) I would like to install a 60amp plug and recepticle. This is a 3 wire with ground. Do the ground and neutral have to be as large as the hot wires. I know that this oven does not need a neutral but the receptical has it and I was going to pull it anyway.
3) Can I get all wires in 3/4 conduit?
4) I would like to use a pigtail from the box to the oven. What type of cord?
Thanks for any advise you can give.
JohnT
This is a commercial oven in a business. The pull would be about 25ft.