    Default Electric Water Heater Side and Back Wall Clearances?

    Installing a 40-gallon electric water heater in my smallish (624 sq' ft') Northern Michigan lake side cottage.

    Space is limited and I wish to build an three sided alcove for the heater in the bathroom.

    What are the side and back wall clearance recommendations, and hazards for a (near) zero clearance.

    Also, is a 30-amp breaker sufficient for a 4500 watt unit, and is a 30-amp switch near the heater also sized correctly and a good idea.

    Thanks.

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,679

    Default

    There are NO clearance limitations for an electric water heater. 30 amp breaker is the standard for residential water heaters, even though they actually only draw about 18 amps. I have only seen a few heaters with a "switch" at the heater, and in the normal course of events it would have limited utility.

  3. #3
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    You must follow the specific instruction manual for YOUR water heater. hj is correct...you will undoubtedly find the the clearance spec for side and back is 0"

    A 25 amp breaker would suffice for a 4500 watt water heater, but since that size breaker is hard to find, they are almost always done on a 30.

  4. #4
    DIY Senior Member DavidTu's Avatar
    Join Date
    Dec 2009
    Location
    Seattle, WA
    Posts
    229

    Default

    My B&W water heater calls for 12" clearance on all sides, I believe. This is for ease of maintenance I assume. So sounds like nothin' in code about it... So I'd be ok with less clearance then, yes?

  5. #5
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,434

    Default

    Keep in mind that the way code is sometimes written, is that you install PER THE MANUFACTURER'S INSTRUCTIONS, so yes, it may require that clearance to pass code...depends on where you are. Also, keep in mind that when that one does die, if there's no clearance, you may be severely restricted in what you replace it with and may need to go through the remodel phase again. They don't last forever!
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

Similar Threads

  1. Side Vent Water Heater
    By scap21 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 08-11-2009, 12:08 PM
  2. toilet clearances to wall and tub
    By handy novice in forum Toilet Forum discussions
    Replies: 2
    Last Post: 05-10-2009, 09:05 PM
  3. Tankless water heater clearances
    By slodog in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 03-07-2008, 10:13 AM
  4. Tankless water heater clearances
    By slodog in forum Tankless Water Heater Forum
    Replies: 3
    Last Post: 03-04-2008, 06:09 AM
  5. 12 gal water heater on It's side????
    By toolaholic in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 10
    Last Post: 10-14-2007, 08:20 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •