    Default Hot Water Issue

    I hate to ask this question because I do see similar ones posted, but here goes...

    I have a Weil McLain WTGO 3L oil boiler that supplies baseboard heat and domestic hot water. Over the past several weeks we have gone from having an ample supply hot water to a trickle of lukewarm water (at best). We actually need to run the shower for 10 minutes before the water warms up. Even then the supply is short lived.

    I think I narrowed the problem to two areas (the mix valve or coil).

    The mix valve is leaking and corroded. I originally thought that the corroded valve was mixing in too much cold water. However, I decided to do further research on the subject before I replaced it.

    While reading older posts, I came to the realization that it could possibly be a bad coil (an idea that I'm leaning towards). Last night while running the shower I touched the hot water line coming from the coil and was able to hold my finger there for several seconds without getting burnt. I assume that under normal circumstances I wouldn't be able to do this, correct? It now seems that warm water is being mixed with cold water.

    Does the issue above sound like a bad coil? I wanted to seek expert advice before I spent the $200 for a replacement.

    The mix valve needs to be replaced regardless...

    Thank you in advance for your advice.

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,405

    Default

    It could be the aquastat...what temp is the boiler at when this happens?
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    DIY Junior Member smangold's Avatar
    Join Date
    Jan 2011
    Location
    PA
    Posts
    2

    Default

    Right now (shower running) the temp is 180. Same thing as usual. I can put my finger on the water line exiting the coil for a few seconds without getting burnt.

    Psi seems to be low, a little under 20.

  4. #4
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,405

    Default

    Internal coils can be problematic and only work on relatively low-flow situations...think hand through a candle flame...move it fast and you never notice.

    You may be better off spending money on an indirect WH, which operates as a separate zone on the boiler.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

Similar Threads

  1. hot water tap issue
    By sukh 31 in forum Shower & bathtub Forum & Blog
    Replies: 6
    Last Post: 11-19-2010, 07:25 AM
  2. GE Refrigerator Ice Maker Water Supply Issue - sprays water into ice cube bin
    By NiceMustang in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 02-04-2010, 07:57 AM
  3. Hot Water Issue
    By Woodward in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 09-03-2009, 06:59 AM
  4. Hot Water Issue
    By Scott-unlv in forum Shower & bathtub Forum & Blog
    Replies: 5
    Last Post: 03-10-2009, 11:07 AM
  5. water pressure issue
    By ohioguy in forum Pumps and Tanks Well Forum & Blog
    Replies: 12
    Last Post: 12-12-2008, 06:06 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •