(206) 949-5683, Top Rated Plumber, Seattle
Results 1 to 3 of 3

Thread: Please check my derating calculations.

Threaded View

  1. #1
    DIY Junior Member rick15752's Avatar
    Join Date
    May 2010
    Location
    California
    Posts
    20

    Default Please check my derating calculations.

    I've been looking for some help on derating and hope someone here can help me.

    Home was built in 1985 and, apparently, derating wasn't closely observed then. But, I've run some new circuits to my breaker panel and I want to make sure I follow the NEC 2008 334.80. Here is my question / situation:

    Top plate at breaker panel, holes for wiring appear to be 1 1/4" in 2x4 framing and are foam sealed. I found two of these holes, containing some 14-2 wire, that allowed me to easily fit more circuits (NM-B) to the panel. I can't drill anymore holes in this stud bay because of other wiring to the panel. I'll reseal with foam.

    What I ended up with:
    Hole #1: three 12-2 plus one 14-2 (each has their own breaker, three 20 amp and one 15 amp)

    Hole #2: two 12-2 plus one 14-2 (each has their own breaker, two 20 amp and one 15 amp)

    Derating calcs:

    Hole #1: 8 ccc
    NEC 310.15(B)(2)(a) 7-9ccc = 70 %
    NEC Table 310.16 Column 90 12ga = 30 amps, 14ga = 25 amps
    30 x .7 = 21.00 amps 20 amp breakers for the three 12 ga wires into the panel
    25 x .7 = 17.50 amps 15 amp breaker for the one 14 ga wire into the panel

    Hole #2: 6 ccc
    NEC 310.15(B)(2)(a) 4-6ccc = 80 %
    NEC Table 310.16 Column 90 12ga = 30 amps, 14ga = 25 amps
    30 x .8 = 24 amps (20 amp breaker for the 12 ga wire)
    25 x .8 = 20 amp (15 amp breaker for the 14 ga wire)

    Are these calculations correct? Should they be calculated separately as done here?
    Last edited by rick15752; 02-09-2011 at 11:42 AM.

Similar Threads

  1. Swing Check vs. dual check vs. double check valve
    By colbymom in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 25
    Last Post: 05-10-2011, 01:19 PM
  2. Derating bundled wires on same circuit
    By rerickson in forum Electrical Forum discussion & Blog
    Replies: 4
    Last Post: 05-22-2010, 12:13 PM
  3. Derating for number of conductors in conduit
    By cacher_chick in forum Electrical Forum discussion & Blog
    Replies: 4
    Last Post: 02-22-2010, 07:49 PM
  4. halogen recessed lighting calculations
    By dabiz7 in forum Electrical Forum discussion & Blog
    Replies: 16
    Last Post: 06-11-2008, 10:42 AM
  5. gas pipe load calculations
    By Yersmay in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 05-11-2008, 08:59 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •