  1. #1
    DIY Member ugabulldog's Avatar
    Join Date
    Nov 2007
    Location
    Northeast GA
    Posts
    60

    Default voltage drop

    Voltage drop was calculated for #10 wire and I am very close (right at) to the max run so I think I will need to size down to #8 wire running 390 ft. to well,....wire in well is 240' of #10 wire, is this ok to mix 8 & 10 to compensate for volt drop?
    Last edited by ugabulldog; 01-20-2011 at 06:16 PM.

  2. #2
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,156

    Default

    Actually having the maximum recommended cable length is a good thing. It makes a natural soft starter. #10 wire will go 630' with a 1 HP motor. It doesn't hurt anything to start with #8, except that it won't give you the soft start like 630' of #10 will do.

    "Reduced-voltage starters may not be required if the maximum recommended cable length is used. With maximum recommended cable length there is a 5% voltage drop in the cable at running amps, resulting in about 20% reduction in starting current and about 36% reduction in starting torque compared to having rated voltage at the motor. This may be enough reduction in starting current so that reduced-voltage starters are not required."

    Heres the link;
    http://www.franklin-electric.com/aim...l/page-36.aspx

  3. #3
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,258

    Default

    I have almost the exact same setup and pump is happy for several years and runs on 239 volts after start up. I may even have a 1.5hp motor on it.

    But where is the control box? at the beginning of the run, or at the well head?

  4. #4
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,156

    Default

    I don't think it will make much difference where the control box is. But I think the starting torque would be less the further away the control box is.

  5. #5
    DIY Member ugabulldog's Avatar
    Join Date
    Nov 2007
    Location
    Northeast GA
    Posts
    60

    Default

    Quote Originally Posted by valveman View Post
    Actually having the maximum recommended cable length is a good thing. It makes a natural soft starter. #10 wire will go 630' with a 1 HP motor. It doesn't hurt anything to start with #8, except that it won't give you the soft start like 630' of #10 will do.

    "Reduced-voltage starters may not be required if the maximum recommended cable length is used. With maximum recommended cable length there is a 5% voltage drop in the cable at running amps, resulting in about 20% reduction in starting current and about 36% reduction in starting torque compared to having rated voltage at the motor. This may be enough reduction in starting current so that reduced-voltage starters are not required."

    Heres the link;
    http://www.franklin-electric.com/aim...l/page-36.aspx
    That is my problem,...I am a little over 630', by a few feet, so I should go with #8, in fear of burning pump up faster, correct?
    Last edited by ugabulldog; 01-22-2011 at 06:57 AM.

  6. #6
    General Engineering Contractor ballvalve's Avatar
    Join Date
    Dec 2009
    Location
    northfork, california
    Posts
    3,258

    Default

    You can mix wire sizes. But the charts have much leeway in them. Dont sweat a few feet.

  7. #7
    DIY Member ugabulldog's Avatar
    Join Date
    Nov 2007
    Location
    Northeast GA
    Posts
    60

    Default

    control box is at the well head, does this make a differnce ballvalve or anyone??

  8. #8
    Well Drilling/Service justwater's Avatar
    Join Date
    May 2010
    Location
    NE FL, SE GA
    Posts
    319

    Default

    it's fine, no worries.

Similar Threads

  1. Wall Socket With Voltage AND No Voltage? HELP!
    By jackvogel in forum Electrical Forum discussion & Blog
    Replies: 2
    Last Post: 12-23-2010, 07:41 AM
  2. Service entrance cable size & voltage drop
    By curtherrin in forum Electrical Forum discussion & Blog
    Replies: 5
    Last Post: 08-24-2009, 12:47 PM
  3. Running low voltage in high voltage boxes
    By Ian Gills in forum Electrical Forum discussion & Blog
    Replies: 10
    Last Post: 08-22-2009, 07:27 PM
  4. Lights flicker and Voltage Drop Question
    By Pip in forum Electrical Forum discussion & Blog
    Replies: 9
    Last Post: 12-18-2008, 06:25 PM
  5. Getting zapped by DC Voltage
    By speedbump in forum Electrical Forum discussion & Blog
    Replies: 7
    Last Post: 01-04-2008, 10:58 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •