Thread: What is a six-unit trap?

  1. #1
    DIY Junior Member seattle_steve's Avatar
    Join Date
    Jan 2011
    Location
    Seattle, WA
    Posts
    28

    Default What is a six-unit trap?

    I'm remodeling and adding a second floor bathroom. King County (Seattle) plumbing code says that a 3" stack can accommodate 48 DFUs, which is more than enough for me. However, there is a footnote that states:

    "Only four water closets or six-unit traps allowed on any vertical pipe or stack..."

    I only have 2 toilets connected to the stack. But I'm confused by "six-unit traps". At first I was reading this as limiting you to "six trap arms" connected to the stack (which would be more than I have planned to connect to the stack -- if you count the toilets). But, now I'm thinking that a "six-unit trap" is something else altogether (like a 4" trap?) and hopefully I don't have to worry about it. Google wasn't much help so I thought I'd ask here.

    Anyone?

    Here's the reference (see footnote "d"):
    http://www.kingcounty.gov/healthserv...nitvalues.aspx

    Thanks.

  2. #2
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    12,406
    Blog Entries
    1

    Default

    A six-unit trap is a 3" trap.
    Your shower uses a 2" 4-unit trap.

    Size of Trap and Trap Arm, Drainage Fixture Unit Values (DFU)

    702.1 for Maximum sizing.

    1-1/4" 1 unit
    1-1/2" 3 units
    2" 4 units
    3" 6 units
    4" 8 units

    From Table 7-3 of the 2009 UPC

  3. #3
    DIY Junior Member seattle_steve's Avatar
    Join Date
    Jan 2011
    Location
    Seattle, WA
    Posts
    28

    Default

    Thanks for the response, Terry. But I'm still a bit confused, because the first table on the King County page I referenced lists a toilet as 3 units and a shower as 2. What am I missing?

    Is there a difference between "fixture units" (which the King County page is defining) and "trap units"? If so, I appreciate the values you provided, but does King County have that documented somewhere? Or is it just in the UPC?

    Thanks.

  4. #4
    DIY Senior Member dlarrivee's Avatar
    Join Date
    Jun 2009
    Location
    Canada
    Posts
    1,173

    Default

    I don't know why you're making this so confusing for yourself.

    There is no unit-trap, no six-trap, no whatever else. Only fixture units.

  5. #5
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    12,406
    Blog Entries
    1

    Default

    The chart comes from the 2009 UPC Code book that Washington State uses.
    I don't know if Canada uses code books, but since the homeowner is Seattle_Steve and has listed the King County web site for information, this will be good information.

    You don't have any 3" p-traps in your home, so I wouldn't worry about it. You normally only see a 3" trap in a commercial situation.
    These are max limits for the trap sizes.

  6. #6
    DIY Junior Member seattle_steve's Avatar
    Join Date
    Jan 2011
    Location
    Seattle, WA
    Posts
    28

    Default

    Ok, thanks Terry. That's good enough for me. (Yes, I'm in Seattle.) Thanks.

  7. #7
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    23,507

    Default

    in the "old days" toilets WERE a 6 unit fixture, but with the low GPF, it has been reduced.

  8. #8
    DIY Junior Member seattle_steve's Avatar
    Join Date
    Jan 2011
    Location
    Seattle, WA
    Posts
    28

    Default

    Ah, now I get it. That totally makes sense hj. Thanks!

  9. #9
    Moderator and Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,003

    Default

    What they are saying is that toilets and showers are "excpetions" to the general rule. They are a larger trap, but with typical volume much less than an application using a 2", or 3", trap in a "regular" way. Just for example, a washing machine places a much bigger load on a 2" trap than does a shower. A shower, nominally, delivers 2.5 gallons per minute. A washing machine can potentiall deliver 10 times that amount

Similar Threads

  1. Replies: 4
    Last Post: 06-23-2010, 05:57 PM
  2. A/C unit in FLA.
    By wallygater in forum HVAC Heating & Cooling
    Replies: 8
    Last Post: 10-27-2009, 03:44 PM
  3. Lav trap on larger trap arm: actual problem?
    By dave148 in forum Plumbing Forum Discussion & Blog
    Replies: 11
    Last Post: 07-07-2008, 07:34 AM
  4. Replace S-trap with P-trap or chicago loop?
    By staceyneil in forum Plumbing Forum Discussion & Blog
    Replies: 4
    Last Post: 03-05-2007, 08:06 AM
  5. Vanity sink trap - can I use 90's after the trap?
    By chassis in forum Plumbing Forum Discussion & Blog
    Replies: 10
    Last Post: 01-16-2006, 06:40 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •