Thread: 2008 NEC/ Closet Lights

Hybrid View

  1. #1
    DIY Junior Member BellPilot's Avatar
    Join Date
    Nov 2007
    Location
    East TN
    Posts
    15

    Default 2008 NEC/ Closet Lights

    Gentlemen,

    I'm in the planning stage of opening up under the interior steps for storage/ closet area. I have a 2005 NEC, which says (if I'm reading right) that recessed fixtures are allowed as long as the bulb is enclosed.

    Anyone know if the 2008 NEC (which my city uses) allows the same?

    Thanks for your time
    Alan

  2. #2
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,522

    Default

    410.16 Luminaires in Clothes Closets.
    (A) Luminaire Types Permitted. Listed luminaires of the following types shall be permitted to be installed in a closet:
    (1) A surface-mounted or recessed incandescent luminaire with a completely enclosed lamp
    (2) A surface-mounted or recessed fluorescent luminaire
    (3) Surface-mounted fluorescent or LED luminaires identified as suitable for installation within the storage area
    (B) Luminaire Types Not Permitted. Incandescent luminaires with open or partially enclosed lamps and pendant luminaires or lampholders shall not be permitted.
    (C) Location. The minimum clearance between luminaires installed in clothes closets and the nearest point of a storage space shall be as follows:
    (1) 300 mm (12 in.) for surface-mounted incandescent or LED luminaires with a completely enclosed light source installed on the wall above the door or on the ceiling
    (2) 150 mm (6 in.) for surface-mounted fluorescent luminaires installed on the wall above the door or on the ceiling
    (3) 150 mm (6 in.) for recessed incandescent or LED luminaires with a completely enclosed light source installed in the wall or the ceiling
    (4) 150 mm (6 in.) for recessed fluorescent luminaires installed in the wall or the ceiling
    (5) Surface-mounted fluorescent or LED luminaires shall be permitted to be installed within the storage space where identified for this use

Similar Threads

  1. 2008 nec question.
    By tig welder in forum Electrical Forum discussion & Blog
    Replies: 8
    Last Post: 05-10-2009, 08:47 AM
  2. Whirlpool - Any Changes in 2008
    By Ray121462 in forum Water Heater Forum, Tanks
    Replies: 20
    Last Post: 02-21-2009, 09:52 AM
  3. antivirus 2008 HELP!
    By cwhyu2 in forum Computers and Stuff
    Replies: 3
    Last Post: 07-14-2008, 07:38 PM
  4. Whirlpool - Any Changes in 2008
    By Ray121462 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 14
    Last Post: 03-29-2008, 03:25 PM
  5. The new 2008 nec.
    By hammerslammer in forum Electrical Forum discussion & Blog
    Replies: 1
    Last Post: 09-26-2007, 04:19 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •