    Default What is a six-unit trap?

    I'm remodeling and adding a second floor bathroom. King County (Seattle) plumbing code says that a 3" stack can accommodate 48 DFUs, which is more than enough for me. However, there is a footnote that states:

    "Only four water closets or six-unit traps allowed on any vertical pipe or stack..."

    I only have 2 toilets connected to the stack. But I'm confused by "six-unit traps". At first I was reading this as limiting you to "six trap arms" connected to the stack (which would be more than I have planned to connect to the stack -- if you count the toilets). But, now I'm thinking that a "six-unit trap" is something else altogether (like a 4" trap?) and hopefully I don't have to worry about it. Google wasn't much help so I thought I'd ask here.

    Anyone?

    Here's the reference (see footnote "d"):
    http://www.kingcounty.gov/healthserv...nitvalues.aspx

    Thanks.

  2. #2
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,191
    Blog Entries
    1

    Default

    A six-unit trap is a 3" trap.
    Your shower uses a 2" 4-unit trap.

    Size of Trap and Trap Arm, Drainage Fixture Unit Values (DFU)

    702.1 for Maximum sizing.

    1-1/4" 1 unit
    1-1/2" 3 units
    2" 4 units
    3" 6 units
    4" 8 units

    From Table 7-3 of the 2009 UPC
    Last edited by Terry; 01-13-2011 at 04:43 PM.

  3. #3
    DIY Junior Member seattle_steve's Avatar
    Join Date
    Jan 2011
    Location
    Seattle, WA
    Posts
    28

    Default

    Thanks for the response, Terry. But I'm still a bit confused, because the first table on the King County page I referenced lists a toilet as 3 units and a shower as 2. What am I missing?

    Is there a difference between "fixture units" (which the King County page is defining) and "trap units"? If so, I appreciate the values you provided, but does King County have that documented somewhere? Or is it just in the UPC?

    Thanks.

  4. #4
    DIY Senior Member dlarrivee's Avatar
    Join Date
    Jun 2009
    Location
    Canada
    Posts
    1,172

    Default

    I don't know why you're making this so confusing for yourself.

    There is no unit-trap, no six-trap, no whatever else. Only fixture units.

  5. #5
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,191
    Blog Entries
    1

    Default

    The chart comes from the 2009 UPC Code book that Washington State uses.
    I don't know if Canada uses code books, but since the homeowner is Seattle_Steve and has listed the King County web site for information, this will be good information.

    You don't have any 3" p-traps in your home, so I wouldn't worry about it. You normally only see a 3" trap in a commercial situation.
    These are max limits for the trap sizes.
    Last edited by Terry; 01-13-2011 at 04:43 PM.

  6. #6
    DIY Junior Member seattle_steve's Avatar
    Join Date
    Jan 2011
    Location
    Seattle, WA
    Posts
    28

    Default

    Ok, thanks Terry. That's good enough for me. (Yes, I'm in Seattle.) Thanks.

  7. #7
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,607

    Default

    in the "old days" toilets WERE a 6 unit fixture, but with the low GPF, it has been reduced.

  8. #8
    DIY Junior Member seattle_steve's Avatar
    Join Date
    Jan 2011
    Location
    Seattle, WA
    Posts
    28

    Default

    Ah, now I get it. That totally makes sense hj. Thanks!

  9. #9
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    What they are saying is that toilets and showers are "excpetions" to the general rule. They are a larger trap, but with typical volume much less than an application using a 2", or 3", trap in a "regular" way. Just for example, a washing machine places a much bigger load on a 2" trap than does a shower. A shower, nominally, delivers 2.5 gallons per minute. A washing machine can potentiall deliver 10 times that amount

Similar Threads

  1. Replies: 4
    Last Post: 06-23-2010, 05:57 PM
  2. A/C unit in FLA.
    By wallygater in forum HVAC Heating & Cooling
    Replies: 8
    Last Post: 10-27-2009, 03:44 PM
  3. Lav trap on larger trap arm: actual problem?
    By dave148 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 11
    Last Post: 07-07-2008, 07:34 AM
  4. Replace S-trap with P-trap or chicago loop?
    By staceyneil in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 03-05-2007, 08:06 AM
  5. Vanity sink trap - can I use 90's after the trap?
    By chassis in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 10
    Last Post: 01-16-2006, 06:40 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •