Thread: Ducane CMPB050U3A fails to light LED Fault Code 3

  1. #1
    DIY Junior Member bigd_1's Avatar
    Join Date
    Nov 2010
    Location
    Maryland
    Posts
    3

    Default Ducane CMPB050U3A fails to light LED Fault Code 3

    Unit has SV9520H Smart Valve which flashes 3 times after a call for heat..
    The Inducer Blower doesn't come on at all.

  2. #2
    DIY Junior Member bigd_1's Avatar
    Join Date
    Nov 2010
    Location
    Maryland
    Posts
    3

    Default

    Following Honeywells guide http://customer.honeywell.com/techli...0s/69-1383.pdf this occurs after the inducer is energized which never happens so I am confused where to look next. The Pressure Switch isn't that expensive but I don't think it is bad and I replaced the inducer already because last year the motor made some noises when starting that made me think it was on the way out so I jumped the gun on replacing it already..

    3 Flashes

    Pressure switch circuit was still sensed as
    open 30 seconds after the inducer was
    energized. System is in 5-minute delay
    mode, with inducer off. After 5-minute delay,
    new ignition sequence is initiated.
    NOTE: SmartValve On/Off switch in OFF
    position during a call for heat generates this
    flash code.

    1. Move SmartValve control switch to ON> Valve is on
    2. Inducer and inducer wiring. Already replace
    3. Low line voltage power supply.
    4. Airflow proving switch operation, tubing, wiring.
    5. Obstructions or restrictions in appliance air intake or
    exhaust flue system that prevent proper combustion air
    flow.
    6. Other devices (such as auxiliary limits) in the airflow
    proving switch circuit.
    Last edited by bigd_1; 11-07-2010 at 07:14 AM.

  3. #3
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Quote Originally Posted by bigd_1 View Post
    this occurs after the inducer is energized which never happens so I am confused where to look next.

    .
    Do you know for sure that the inducer is never energized, or is it that the inducer motor is bad? That is the whole point of the pressure switch....to prove that the blower is running.

    Since this is not a new system, and used to work, we can assume that the line voltage polarity is correct, but it it worth checking. For sure it is worth checking that the grounds are still good. This system is sensitive to polarity and good ground.

    Failures in complex system are often by visual or simple tests of "the basics"

  4. #4
    DIY Junior Member bigd_1's Avatar
    Join Date
    Nov 2010
    Location
    Maryland
    Posts
    3

    Default

    yes i know for sure and this is a new inducer
    i am thinking it is the fan timer

  5. #5
    DIY Junior Member marcar's Avatar
    Join Date
    Jan 2011
    Location
    Sumner , IL
    Posts
    1

    Default

    could be your fan timer could also be the sv9520h valve.

Similar Threads

  1. Ducane furnace will not light then shuts down
    By Dean M in forum HVAC Heating & Cooling
    Replies: 2
    Last Post: 09-28-2010, 02:52 PM
  2. Subdrive 150 flashing red fault light.
    By whotheguy in forum Pumps and Tanks Well Forum & Blog
    Replies: 19
    Last Post: 12-28-2009, 10:49 AM
  3. Fan required to turn on with light required by Code ?
    By Scuba_Dave in forum Shower & bathtub Forum & Blog
    Replies: 11
    Last Post: 12-18-2009, 09:20 AM
  4. fault code for a centurion heating system
    By w1ljm in forum HVAC Heating & Cooling
    Replies: 1
    Last Post: 12-15-2009, 07:20 PM
  5. 3 Way Switch power fails at Light
    By BigSkeet in forum Electrical Forum discussion & Blog
    Replies: 10
    Last Post: 07-10-2008, 06:05 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •