Oversizing isn't usually as big an issue with mod-cons until/unless it's RIDICULOUSLY oversized. (You didn't buy the Alpine -150 or -285, I hope? The -80 and -105 would be enough boiler for about 90% of the single-family homes in NY.) The min-modulated input of the Alpine 80 is ~16KBTU/hr, max is ~80K. Almost any house but a superinsulated house will have at least a 15k load at 20-25F outside temps.
You DO need to run it a modulation level & temperature where the radiation can give up that amount heat to the house though. You can set it to 120F out and if the baseboards are short enough that they only deliver 8-9K to the house at that temp range it'll short-cycle, even at minimum fire. If it's running higher than min with a small delta-T between output and return, with a ball-valve in the loop you could carefully reduce the flow until it's running at the minimum modulation at the output temp you've set.
Some boilers can be programmed to run at min-mod only as a test to determine the temperature at which it'll short-cycle with the given flow rate, and it appears the Alpine does too (see figure 38, upper left :
http://s3.pexsupply.com/manuals/1249...2-01_Feb08.pdf ) If you leave the boiler off for a good half hour, then start it in min-modulation mode, the temperature it reaches after about 10-12 minutes is pretty much the minimum temp below which it would otherwise short-cycle, so set your reset curve minimums accordingly. (The note says that it automatically reverts to modulation mode after 15 minutes if you put it in the min-mod test mode.) If the return water temp is out of the condensing range (well above 120F on the return), then it's probably worth adding a tank to buffer it so that it can be run at lower temp without short cycling. This is a 15 minute test- you can tweak the rest of the curve later after you've moved in, but stopping the short-cycling saves a lot of wear & tear on the boiler.
Since this is a new heating system design, hopefully the designer maxed out the baseboard length to ensure that it can deliver design-day heat in the condensing zone most of the time, and without short-cycling issues. Baseboard is so CHEAP that it should be a crime to design a system that needs 180F on design-day, since for less than $20/foot it can be lengthened 50% and be able to deliver it at 140F, with 120F return. Of course it's always possible to run out of wall-length, at which point flat-panel radiators start looking more attractive despite the higher price. (They're definitely more comfortable than fin-tube baseboard, comparable or better comfort than cast-iron baseboard.)