Originally Posted by
Dana
David1: The boiler only has one loop- putting the electric tank in series with either the output or return side (between the zone manifold & boiler) would allow the mass to participate in every burn, independently of how the rest of the system is configured. A short section of 3/4" plumbing on the boiler loop isn't going to present enough head to ANY pump to cause issue with operation of the boiler at the flows you'll be looking at. The 1" taps are only necessary to be able to run it on longer runs at full-fire without running out of margin on the safe delta-T. (see discussion below) The tank is a lot fatter than 3/4"- so you're really only looking at the length of the tank's dip-tube.
300' of fin-tube is capable of delivering ~75KBTU/hr with 120F average water temps, so with your zones are split evenly 150' would still be above min-mod, you should be able to run ~125 or 130F output water without inducing short-cycles, but you may need to reduce the flow (tweaked with a ball valve) to get it to actually RUN at mininum moduation. As long as the return water is ~120F or below you'll be in the 90%+ range. If it doesn't allready have a ball valve in series with each zone, adding ball valves to be able to back off the flow and tweaking each zone to run the boiler at min-mod when it's the only zone calling for heat is much easier & cheaper than adding a buffer tank on the boiler loop- I'd go there first. With that much fin tube in you should be able to achieve continuous burns whenever there's a call for heat (from either or both zones) and stay in condensing mode the entire time.
Combustion efficiency in condensing boilers is all about the return water temp- if you can get it to run 100-110F return-water into the boiler and 120-130F out you'll be in the mid-90s. I'm not sure what the max delta between output and return the Alpine is speced for, but 20-30F deltas are safe for any boiler. At 2gpm a 30F delta between output & return is ~30KBTU/hr, so that's a decent way to guage when you're balanced at or near mid-mod you are when tweaking flows. Even if you have to bump up the output up 140F out with 110F return for consistent heat in every room that's still fully condensing, but 140F out with 120F water on the return would be a few percent lower efficiency.
While 6 minute burns aren't exacting terrible toll on efficiency on a low-mass boiler, reducing the number of burn cycles by a factor of 2 or 3 saves considerable wear & tear, and you can probably get there without adding mass with 150' of fin-tube per zone.
Most heat loss calcs tend to run 25-35%on the high-side of reality- you may actually be closer to 50K. If you have a year's worth of fuel use to work against weather data you can get closer to the true design-condition heat load, but that won't much change how you set up the system. Average water temps still need to be in the 120F range for consistency with fin-tube, and that's more than enough to meet design-day conditions at 120F AWT.