    Default Safe to Remove Dryer Lockout?

    We just bought a house that previously had a gas dryer installed. It's been removed, the gas line capped, and we're ready to hook up our electric dryer. The circuit breaker has a lockout installed over the dryer breakers (see attachment).

    My thinking - since the previous owner had gas (haha), an electrician put the lockout in place since the dryer outlet wasn't needed. I'd like to pop it off and start drying clothes again, but obviously have safety in mind first.

    Any thoughts on removing it, or a quick test to determine safety?

    Thanks,
    BigSkeet
    Attached Images Attached Images  

  2. #2
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    That is NOT a lockout. It is a handle tie on a quad breaker. Just push it to the ON position and you'll have power.

  3. #3
    DIY Junior Member BigSkeet's Avatar
    Join Date
    Feb 2008
    Location
    Chapel Hill, NC
    Posts
    10

    Default

    Thanks for the quick response. UNfortunately it (or something) is preventing it from being pushed into the on position. I can push it there, but it won't hold, just pops back to the middle position each time.

  4. #4
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Then you have a problem. Something is tripping the breaker. Unplug your dryer and try it again and let us know what happens

  5. #5
    DIY Junior Member BigSkeet's Avatar
    Join Date
    Feb 2008
    Location
    Chapel Hill, NC
    Posts
    10

    Default

    I popped off the handle tie and was able to move them both back to on position, but no juice. I cut them back off. Then again...

    File this under "things that would be helpful for you to know upfront": I had to remove the dryer's existing 4 prong connection and replace it with a 3 prong dryer connection. No big deal...done it before. To make sure I had the right fit, I plugged in the 3 prong before wiring it up to the dryer. Not wise. Because the contacts on the other end of the plug were touching one another , I got a nice little spark. I'm thinking I've fried the socket itself, and that's the cause of the inability to restore power.

  6. #6
    DIY Senior Member dlarrivee's Avatar
    Join Date
    Jun 2009
    Location
    Canada
    Posts
    1,172

    Default

    Wow... You should probably take a lot more care in any electrical you mess with.

  7. #7
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,140

    Default

    I believe a proper 4- wire circuit is a code requirement when installing a new drier.
    I know that IS true when installing a stove.

  8. #8
    Electrical Contractor jbfan74's Avatar
    Join Date
    Jun 2007
    Location
    Newnan, GA
    Posts
    129

    Default

    Well, you have just created more problems for yourself!
    Yes I am A Pirate-Jimmy Buffett

  9. #9
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    It is OK to connect a dryer to an existing 3 prong outlet. BUT, you must carefully read the installation instruction that come with the dryer...it will be necessary to change the arrangement of the ground connection inside the dryer.

    The clip on the breaker is to make it a double pole...if one trips it takes the other one with it. DO NOT remove the clip.

  10. #10
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    Quote Originally Posted by BigSkeet View Post
    I popped off the handle tie and was able to move them both back to on position, but no juice. I cut them back off. Then again...

    File this under "things that would be helpful for you to know upfront": I had to remove the dryer's existing 4 prong connection and replace it with a 3 prong dryer connection. No big deal...done it before.
    YES, big deal! Put the four prong receptacle back in and get you a four wire dryer cord. THIS is the code legal and safe thing to do.

    Quote Originally Posted by BigSkeet View Post
    To make sure I had the right fit, I plugged in the 3 prong before wiring it up to the dryer. Not wise. Because the contacts on the other end of the plug were touching one another , I got a nice little spark. I'm thinking I've fried the socket itself, and that's the cause of the inability to restore power.
    Wow.

  11. #11
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,382

    Default

    Someone has written what looks like "Stove" between the dryer. Could they have put in an electric stove or oven and used those leads for that? If so, adding the dryer back into the circuit would overload it when both are on. I'm somewhat concerned that the two breakers don't move freely enough to turn them on - will one trip the other if required?
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  12. #12
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    Quote Originally Posted by jadnashua View Post
    Someone has written what looks like "Stove" between the dryer. Could they have put in an electric stove or oven and used those leads for that? If so, adding the dryer back into the circuit would overload it when both are on. I'm somewhat concerned that the two breakers don't move freely enough to turn them on - will one trip the other if required?
    That is a quad breaker. Two 240v circuits in the place of two full size breakers.
    The "stove" is the inner 30A/240v circuit on that breaker. The dryer is the outer circuit.

  13. #13
    Electrical Contractor jbfan74's Avatar
    Join Date
    Jun 2007
    Location
    Newnan, GA
    Posts
    129

    Default

    Quote Originally Posted by Speedy Petey View Post
    That is a quad breaker. Two 240v circuits in the place of two full size breakers.
    The "stove" is the inner 30A/240v circuit on that breaker. The dryer is the outer circuit.
    I have seen them in homes, but mostly inside mobile homes
    Yes I am A Pirate-Jimmy Buffett

  14. #14
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    Quote Originally Posted by jbfan74 View Post
    I have seen them in homes, but mostly inside mobile homes
    Yup. 200A 20/40 space panels right. Don't you love them.

Similar Threads

  1. How Safe Is Riddex, Rid-X
    By thecropchick in forum Toilet Forum discussions
    Replies: 2
    Last Post: 04-11-2009, 06:30 PM
  2. Is this safe/compliant/doable?
    By beekerc in forum Electrical Forum discussion & Blog
    Replies: 4
    Last Post: 01-15-2009, 04:24 AM
  3. Is it safe to fertilize with a private well?
    By nickyg in forum Pumps and Tanks Well Forum & Blog
    Replies: 1
    Last Post: 04-30-2006, 05:21 PM
  4. Is it safe to weir a rubber?
    By prashster in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 02-17-2006, 05:31 AM
  5. Polybutelene(PB) - is the new PB safe
    By STEVEH in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 11-27-2004, 09:47 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •